Boilermate 2000 High Gas Usage

3 posters

Go down

Boilermate 2000 High Gas Usage Empty Boilermate 2000 High Gas Usage

Post  jumper4 Sun May 18, 2014 4:16 pm

Hi all
I recently had my A.C.B changed on the Boilermate 2000 to a GT155
Now my gas bill has doubled
I took a look and found only 1 jumper on No4 (I believe this is standard for a replacement board) and Jumpers for this model should be on 1 3 and 4
would this effect my gas usage by so much or do you think there might be another problem.
Thanks in advance

jumper4

Posts : 2
Join date : 2014-05-18

Back to top Go down

Boilermate 2000 High Gas Usage Empty Re: Boilermate 2000 High Gas Usage

Post  mike Tue May 20, 2014 1:37 pm

Should be on 1,3 and 4.
When fitting put one on 5.
Switch on.
It will goes through a routine.
When ON shows on display.
Switch off supply, remove jumper from 5 and all done.
Mike

mike

Posts : 1747
Join date : 2009-10-08
Age : 70
Location : Norwich

http://www.mgch20.co.uk

Back to top Go down

Boilermate 2000 High Gas Usage Empty Re: Boilermate 2000 High Gas Usage

Post  jumper4 Mon May 26, 2014 5:25 pm

Thanks Mike for the reply
jumpers set with no errors but burning gas like a good'en
using ideal boiler set to max but whole house is burning up with the heat
heating turned off just hot water but the heat is pretty unbearable. running around 100kw a day when should be about 30kw
do you think it's maybe a duff board or scaled on a sensor as boilermate always seems to be asking boiler to switch on very often.
Thanks

jumper4

Posts : 2
Join date : 2014-05-18

Back to top Go down

Boilermate 2000 High Gas Usage Empty Re: Boilermate 2000 High Gas Usage

Post  Mario.S Tue May 27, 2014 12:47 am

jumper4 wrote:Thanks Mike for the reply
jumpers set with no errors but burning gas like a good'en
using ideal boiler set to max but whole house is burning up with the heat
heating turned off just hot water but the heat is pretty unbearable. running around 100kw a day when should be about 30kw
do you think it's maybe a duff board or scaled on a sensor as boilermate always seems to be asking boiler to switch on very often.
Thanks

Hi Jumper
As on all 2000 type appliance, with the standard factory set jumper (in position 4), the pcb do not know, if you have a Boilermate or Systemate or Gulfstream. From this of course, it will operate in “ backup mode” means, heating on all time with no control, hot water on all time, boiler pump on all time, boiler call on all time .
If you still have the old PCB, use the jumper from there to set your pcb correct or alternatively, go to a computer shop and ask for some jumper ( only sum pence) to set your pcb. Switch the Boilermate of, set the jumper, and switch back on again.
Kind regards Master Mario at Mario’s Boiler Service

Mario.S

Posts : 224
Join date : 2011-12-10
Location : Fareham / Hampshire

http://www.marios-boiler-service.co.uk/

Back to top Go down

Boilermate 2000 High Gas Usage Empty Re: Boilermate 2000 High Gas Usage

Post  Sponsored content


Sponsored content


Back to top Go down

Back to top

- Similar topics

 
Permissions in this forum:
You cannot reply to topics in this forum