boilermate3 no divertor valve supply

2 posters

Go down

boilermate3 no divertor valve supply Empty boilermate3 no divertor valve supply

Post  rosieposie Wed May 28, 2014 1:39 pm

hi ,
I recently got asked by a friend to look at their boilermate 3 which has ceased to function , after conducting some tests and speaking to Gledhill it appeared there was no switch supply to the boiler , thus it was decided the pcb was damaged which I changed , that supply has now been restored but the divertor valve still doesn't operate , there is no output on any of the switch lives to the valve to make it operate from the pcb , something which also appeared to be present on the old damaged board , is there any thing I should be checking that's stopping the valve supply from the board ?
cheers

rosieposie

Posts : 2
Join date : 2014-05-28

Back to top Go down

boilermate3 no divertor valve supply Empty Re: boilermate3 no divertor valve supply

Post  Mario.S Wed May 28, 2014 2:43 pm

Hi
Try to feed the gray switch live2 from the motor valve ( pcb terminal 14) direct to the room stat call on the pcb ( terminal 28) , if there is any response then. If this is the BM3 with single pcb (GT155).
Hope this helps
Regards Master Mario at Mario’s Boiler Service

Mario.S

Posts : 224
Join date : 2011-12-10
Location : Fareham / Hampshire

http://www.marios-boiler-service.co.uk/

Back to top Go down

boilermate3 no divertor valve supply Empty Re: boilermate3 no divertor valve supply

Post  Mario.S Wed May 28, 2014 2:45 pm

Have you also checked the jumper position?
Regards Master Mario at Mario’s Boiler Service

Mario.S

Posts : 224
Join date : 2011-12-10
Location : Fareham / Hampshire

http://www.marios-boiler-service.co.uk/

Back to top Go down

boilermate3 no divertor valve supply Empty Re: boilermate3 no divertor valve supply

Post  Mario.S Wed May 28, 2014 2:50 pm

If this works, you could then also put the boiler SL ( terminal 7 ) together with the SL1 ( brown ( terminal 13)
Regards Master Mario at Mario’s Boiler Service

Mario.S

Posts : 224
Join date : 2011-12-10
Location : Fareham / Hampshire

http://www.marios-boiler-service.co.uk/

Back to top Go down

boilermate3 no divertor valve supply Empty Re: boilermate3 no divertor valve supply

Post  rosieposie Fri May 30, 2014 12:48 pm

im going to have a look at these options tomorrow ,
can I ask what the jumper position should be , the old board just had one on position 4 ,

rosieposie

Posts : 2
Join date : 2014-05-28

Back to top Go down