CHANGE OF TEMEPATURE

Post  os0dgi on Wed Jun 17, 2009 9:58 am

Hello, The pump was recently replaced by a local plumbing company but we have the problem with the temparature of the water which changes between hot and cold. The company which replaced the pump says that it is the corroded 'back plate' which needs to be replaced. Another company, however, said that the replacement pump - Grundfos 15/50 domestic hot water circulation pump, Red colour- is wrong one and that is the cause of the temparature problem. I am very confused and it would be great if you could give some advise on this. Thank you!

os0dgi

Posts : 1
Join date : 2009-06-17

View user profile

Back to top Go down

Re: CHANGE OF TEMEPATURE

Post  Mike the Boilerman on Thu Jul 02, 2009 2:57 pm

Hi os0dgi,

The pump you have is the correct pump, but unfortunately it did not need to be changed. The corroded back plate on the old one would most definitely NOT have caused the symptoms you describe! It will be a failing DHW heat sensor.


Cheers, Mike

Mike the Boilerman
Admin

Posts : 426
Join date : 2009-01-08

View user profile http://gledhill-repairs.forumotion.net

Back to top Go down

The pump

Post  sunny.sahdev on Mon Oct 14, 2013 9:51 am

The pump may not be correct. Grundfos supply a range of 15-50 pumps but more specifically you need a 15-50x18 pump.

sunny.sahdev

Posts : 383
Join date : 2013-08-21
Age : 31
Location : Vedhas Limited, 960 Capability Green

View user profile http://www.vedhas.co.uk/vedhas-what-we-do/pulsacoil-repair/#

Back to top Go down

Re: CHANGE OF TEMEPATURE

Post  Sponsored content


Sponsored content


Back to top Go down

View previous topic View next topic Back to top

- Similar topics

 
Permissions in this forum:
You cannot reply to topics in this forum