No hot water
Page 1 of 1
No hot water
Hi
I have a 15 year old Boilermate 3 that I have replaced the plate heat exchanger in about 6 year ago and a pcb control board about 2 years ago. Today I fitted a new towel heater radiator and the DHW has stopped working. The water runs hot for about 30 seconds then goes cold. The DHW pump is coming on as I can feel it gently vibrating.
When I removed the old radiator I did drain it first and obviously filled the new one today.
I wondered if the storage tank hadn't filled enough although I don't think one small radiator would drop the water level much. So I investigated the header tank and found a useless ball valve which was completely stuck closed. So I topped the header tank up with a jug without benefit, the header was half full, well over the storage tank inlet.
The heating works fine.
Any trouble shooting suggestions?
Best wishes
Phil
I have a 15 year old Boilermate 3 that I have replaced the plate heat exchanger in about 6 year ago and a pcb control board about 2 years ago. Today I fitted a new towel heater radiator and the DHW has stopped working. The water runs hot for about 30 seconds then goes cold. The DHW pump is coming on as I can feel it gently vibrating.
When I removed the old radiator I did drain it first and obviously filled the new one today.
I wondered if the storage tank hadn't filled enough although I don't think one small radiator would drop the water level much. So I investigated the header tank and found a useless ball valve which was completely stuck closed. So I topped the header tank up with a jug without benefit, the header was half full, well over the storage tank inlet.
The heating works fine.
Any trouble shooting suggestions?
Best wishes
Phil
gasdoc- Posts : 17
Join date : 2011-02-27
All sorted
New F&E tank ball valve
New PHE
New cold feed (as per Mike's instructions)
Many thanks for this most excellent forum Mike!
New PHE
New cold feed (as per Mike's instructions)
Many thanks for this most excellent forum Mike!
gasdoc- Posts : 17
Join date : 2011-02-27
Similar topics
» Pulsacoil 2000 -Hot water in the thermal store but cold water from the taps.
» Only short blasts of hot water in the morning, rarely hot water in the afternoon/evening
» No hot water, red fault light on, after adjusting thermostat
» Gledhill Boilermate Class A OV - PHE (hot water) pump constantly whirring, but no hot water
» Poss reason for no hot water - Check the water level at the top of the unit
» Only short blasts of hot water in the morning, rarely hot water in the afternoon/evening
» No hot water, red fault light on, after adjusting thermostat
» Gledhill Boilermate Class A OV - PHE (hot water) pump constantly whirring, but no hot water
» Poss reason for no hot water - Check the water level at the top of the unit