Pulsacoil 2000 pump continously running!
2 posters
Page 1 of 1
Pulsacoil 2000 pump continously running!
I wonder if any body can help me I have a pulsacoil 2000 and have replaced pump with correct grundfos pump but pump constantly runs have changed both phe and dhw sensor and PCB but pump continues to run and gets extremely hot, I'm having turn it off and just heat up and use water as and when i need it, please can somebody help me!!!
Arceye- Posts : 3
Join date : 2016-11-15
Re: Pulsacoil 2000 pump continously running!
Is the XB004 pump?
Not just any Grundfos pump will do.
Sensor connection in their correct places?
Bled the pump when you fitted.
If not the pump drive PCB is faulty
Mike
Not just any Grundfos pump will do.
Sensor connection in their correct places?
Bled the pump when you fitted.
If not the pump drive PCB is faulty
Mike
Problem sorted
Solved the problem found that the phe & dhw sensors earth wires was wired into where the phe sensor neutral wire was supposed to be and the neutral phe sensor wire was in where the earths should be!!. After wiring this in right the pcb was wrecked and didn't work so replaced board with a secondhand and it now works perfectly now.
This has been wired up wrong for 11 YEARS!!, no wonder I've had problems with it!
Thanks for the advice though Mike
This has been wired up wrong for 11 YEARS!!, no wonder I've had problems with it!
Thanks for the advice though Mike
Arceye- Posts : 3
Join date : 2016-11-15
Re: Pulsacoil 2000 pump continously running!
Lol
Never assume all is correct!
Had that lots of times.
More so with BM 2000 sensors.
Wired up wrong.
Well done
Mike
Never assume all is correct!
Had that lots of times.
More so with BM 2000 sensors.
Wired up wrong.
Well done
Mike
Similar topics
» Pump not running Pulsacoil 2000
» BoilerMate 2000 No hot water in the mornings when boiler turned on, HW pump runs continously when up to temp.
» Pump still running on boilermate 2000
» PSB and Pump replaced Pump humming and getting hot
» what can be the problem? pulsacoil III; noisey PCB, constant running pump
» BoilerMate 2000 No hot water in the mornings when boiler turned on, HW pump runs continously when up to temp.
» Pump still running on boilermate 2000
» PSB and Pump replaced Pump humming and getting hot
» what can be the problem? pulsacoil III; noisey PCB, constant running pump
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum
|
|