boilermate 2000

View previous topic View next topic Go down

boilermate 2000

Post  jdk67 on Mon Aug 03, 2009 2:53 pm

hi all i have recently fitted a boilermate 2000 with a worcester 24i system boiler hot water seems fine but cant get central heating to work the over ride works the heating but no joy when set back to normal operation there seems to be no power to the room stat from the board any help would be greatly recieved.
thanks
james

jdk67

Posts : 1
Join date : 2009-08-03

View user profile

Back to top Go down

Re: boilermate 2000

Post  Midland Boilercare on Sat Aug 15, 2009 2:15 am

There are a number of potential options for this, but the first that you should check is that the boiler thermostat is set to MAXIMUM.
The Boilermate will not allow central heating until the store reaches a minimum of 60deg C (the heating pump will not activate below this temp).
Also check the internal time clock as the room stat is wired in series with this.

Regards
Dave Hickey
Midland Boilercare Ltd