Manual operation of controls blows a fuse

View previous topic View next topic Go down

Manual operation of controls blows a fuse

Post  tarka999 on Wed Feb 04, 2009 1:33 pm

After having a problem with my Boiler mate 2000 I rsorted to using the manual overide knob on the front panel. However this has the result of blowing the small internal fuse FS3 5 amp. Replaced it and tried again. Same thing. Any help would be appreciated

tarka999

Posts : 1
Join date : 2009-02-04

View user profile

Back to top Go down

Re: Manual operation of controls blows a fuse

Post  Mike the Boilerman on Fri Feb 06, 2009 2:59 am

Hi tarka999,

The fuse blowing is usually caused by water ingress into a pump motor. I suggest checking the pumps extremely carefully before replacing the fuse, and replacing any pump with evidence of water marks around the control box, because this fault usually blows a triac on the control board instead of the fuse!

The water orginates from the pump isolating valves which leak.

Cheers, Mike



tarka999 wrote:After having a problem with my Boiler mate 2000 I rsorted to using the manual overide knob on the front panel. However this has the result of blowing the small internal fuse FS3 5 amp. Replaced it and tried again. Same thing. Any help would be appreciated

Mike the Boilerman
Admin

Posts : 426
Join date : 2009-01-08

View user profile http://gledhill-repairs.forumotion.net