Boilermate 2000 hot water
2 posters
Page 1 of 1
Boilermate 2000 hot water
Hi there,
I am working on a Boilermate 2000 and seeing as i have not come across these before, i thought i would ask the professionals.
The water to the taps & shower mixer cycle from hot to cold. This is only for a few seconds, then it will get really hot and stay like that for a while and then go again.
I thought it may have been the heat exchanger at first, but i was wandering about the hot water sensors?.
The pump for the hot water runs intermitantly, but sounds like the pump is not running all the time that the hot water is running, making a buzzing sound.
My thoughts were that the pump was on it's way out.
The water pressure is very high, not checked the incoming pressure yet.
I know these boilers are rated to 3 bar, so anything above that could it be a problem to this type of boiler?
Any information would be greatly received.
Regards
I am working on a Boilermate 2000 and seeing as i have not come across these before, i thought i would ask the professionals.
The water to the taps & shower mixer cycle from hot to cold. This is only for a few seconds, then it will get really hot and stay like that for a while and then go again.
I thought it may have been the heat exchanger at first, but i was wandering about the hot water sensors?.
The pump for the hot water runs intermitantly, but sounds like the pump is not running all the time that the hot water is running, making a buzzing sound.
My thoughts were that the pump was on it's way out.
The water pressure is very high, not checked the incoming pressure yet.
I know these boilers are rated to 3 bar, so anything above that could it be a problem to this type of boiler?
Any information would be greatly received.
Regards
Bluemax32000- Posts : 3
Join date : 2010-04-14
Re: Boilermate 2000 hot water
Hi Bluemax
Sorry for the late reply to this post. if the repair hasn't been completed yet, it would seem to me that either the hot water or the PHE sensors are causing the problem.
Check the readings on the display panel. Any reading that says Err indicates a faulty sensor.
Kind regards
David Hickey
Midland Boilercare Ltd
service@midlandboilercare.co.uk
Sorry for the late reply to this post. if the repair hasn't been completed yet, it would seem to me that either the hot water or the PHE sensors are causing the problem.
Check the readings on the display panel. Any reading that says Err indicates a faulty sensor.
Kind regards
David Hickey
Midland Boilercare Ltd
service@midlandboilercare.co.uk
Similar topics
» Boilermate 2000 no hot water
» Boilermate 2000 No Hot Water
» New house with Boilermate 2000. No hot water
» BoilerMate 2000 Sometimes we have hot water sometimes nothing. (Norfolk)
» Boilermate 2000 hot water problem
» Boilermate 2000 No Hot Water
» New house with Boilermate 2000. No hot water
» BoilerMate 2000 Sometimes we have hot water sometimes nothing. (Norfolk)
» Boilermate 2000 hot water problem
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum