Boilermate 3

Post  Kevin on Tue Feb 10, 2009 6:14 am

Hi we have been without hot water for about a week now.It seems that there is no hot water in the tap or shower,the shower runs warm for about 1 minute then goes cold.The boiler down stairs seems to be working because the flame comes on as it should.What advice can you give me any would be a help,we live in the North East of England.

Kevin

Posts : 4
Join date : 2009-02-10

View user profile

Back to top Go down

Re: Boilermate 3

Post  Mike the Boilerman on Tue Feb 24, 2009 1:37 am

Hi Kevin,

If the central heating works then we know the Boilermate is warming up correctly. Does it?

If it does, we next need to find out if the HW pump runs when you turn a hot tap ON. Does it?

If yes, then it's probably blender valve failure. If not, then it's probably sensor failure or flow switch failure.

Hope that helps, but unfortunately there is no substitute for being in front of the appliance when homing in on a fault!

Cheers, Mike

Mike the Boilerman
Admin

Posts : 426
Join date : 2009-01-08

View user profile http://gledhill-repairs.forumotion.net

Back to top Go down

Re: Boilermate 3

Post  Kevin on Tue Mar 24, 2009 1:36 pm

thanks for the sugestion about the cold water pipe bypass it worked a treat cost about 350 pounds and hopefuly will keep us in hot water.

Kevin

Posts : 4
Join date : 2009-02-10

View user profile

Back to top Go down

Re: Boilermate 3

Post  Mike the Boilerman on Wed Mar 25, 2009 2:42 pm

Hi Kev,

You're welcome!

Cheers, Mike

P.S. what suggestion was that then? ;-)

Mike the Boilerman
Admin

Posts : 426
Join date : 2009-01-08

View user profile http://gledhill-repairs.forumotion.net

Back to top Go down

Re: Boilermate 3

Post  Sponsored content


Sponsored content


Back to top Go down

View previous topic View next topic Back to top

- Similar topics

 
Permissions in this forum:
You cannot reply to topics in this forum