Cold showers unless "switch" is used

2 posters

Go down

Cold showers unless "switch" is used Empty Cold showers unless "switch" is used

Post  petew Tue May 05, 2009 1:03 pm

Hi there,
Hope you can help with the following problem.
Central heating works fine but the shower runs cold unles the "switch" is turned on.
Also have low hot water pressure pressure when more than one thing is turned on.

Any advice greatly appreciated.

petew

petew

Posts : 3
Join date : 2009-05-05

Back to top Go down

Cold showers unless "switch" is used Empty Re: Cold showers unless "switch" is used

Post  Mike the Boilerman Sun May 31, 2009 4:48 pm

Hi Pete,

Probably sensor failure, but could be a scaled up heat exchanger if flow is poor.

I'd need to see it to say which though.

Cheers, Mike

Mike the Boilerman
Admin

Posts : 446
Join date : 2009-01-08

https://gledhill-repairs.forumotion.net

Back to top Go down

Cold showers unless "switch" is used Empty Re: Cold showers unless "switch" is used

Post  petew Sun Jul 19, 2009 10:28 am

Hi Mike,
I've replaced the pump speed sensor and the plate heat exchanger and everything now working fine.

Many thanks.