No heating
I am not an engineer of any sort. The boiler is firing, set to max. Hot water is fine. Room themostat is set to 30 as hoping to give it a boost. All radiators are cold. Boiler fires up every now and again but doesn't stay on for long. Help! please.
Mimatron- Posts : 14
Join date : 2011-10-24
Re: No heating
I believe that you checked this topic but just in case not - "Boilermate 2000 + Potterton Suprima = No heating"
scorp- Posts : 77
Join date : 2010-07-07
Re: No heating
Then only one part can be interesting for you "It is essential that the boiler thermostat is turned up to maximum as the Boilermate 2000 won't let the central heating work unless it is hotter than 60deg C.".
For more help you probably need to be a bit DIY. Hope more experienced gurus will give here advices
For more help you probably need to be a bit DIY. Hope more experienced gurus will give here advices
scorp- Posts : 77
Join date : 2010-07-07
No heating
How do i check the temperature? I have everything i can on full blast all radiators turned on too. Thanks for all your help Scorp.
Mimatron- Posts : 14
Join date : 2011-10-24
no heating
Another thing my 'switch' doesn't work either, still no heating. In the past we have called heating specialists in and they don't have a clue when they see the Gledhill unit.
Mimatron- Posts : 14
Join date : 2011-10-24
Re: No heating
As I said I'm not professional in it(only know electronics) but if nobody answer then may i suggest that you need to open front panel of Boilermate and look at PCB. I think that when you turn everything for heating on then green LED for CH pump will light up. If it will but pump doesn't start then it may be either PCB or pump itself. LED position you can find in manual. Also you can check temperature which must be higher than 60C as mentioned in the post i provided. Also you may check signals on PCB to make sure that thermostat and timer really switch CH but I suspect if "switch-emergency" doesn't override then it is not thermostat/timer problem. But you need to be "DIY" for it and careful because PCB has high voltage. So if you think you cannot do it then better to call local gledhill specialist.
By the way, it also may be the temperature sensors but i don't know how to check them, could be by reading temperature on PCB display, not sure
By the way, it also may be the temperature sensors but i don't know how to check them, could be by reading temperature on PCB display, not sure
scorp- Posts : 77
Join date : 2010-07-07
no heating
Ok thanks again, I will try this over the weekend.
Mimatron- Posts : 14
Join date : 2011-10-24
Re: No heating
Hi,
Have you checked that with the heating on and the thermostat asking for heat that you have 230volts and the CH Pump?
Regards
Gary
MK Group Ltd
Have you checked that with the heating on and the thermostat asking for heat that you have 230volts and the CH Pump?
Regards
Gary
MK Group Ltd
no heating
I took the front panel off. Don't know what a PCB is could only fine an ACB, hardwater Appliance Control Board. I can't find anything which tells me what the temp is.
Red pump in middle, Space heating pump (is this central heating?)has a little bit of rust on the paste/cement which was used on it. Can't see any leaks or anything. On the ACB panel there are 4 LED lights in a column, top light was off when I took panel off. Switched to emergency back up, all lights went out. When i switched back, top LED light was out others came on. There is a small panel with red LED writing which says 'ON' to the left of it are 2 red lines.
to MK Group Ltd - I assume we have 230 v but don't know how to check, i am in no way an engineer of any sort! Not sure waht you mean by "and the CH Pump?".
This is so frustrating as it could be something so simple and i may end up paying loads of money for a 5 min job! Done this before, charged a £100 by a 'Gledhill Specialist' who didn't even fix it. He charged me for all the phone calls he made to the Gledhill company, guess I was naive, shouldn't have paid.
Red pump in middle, Space heating pump (is this central heating?)has a little bit of rust on the paste/cement which was used on it. Can't see any leaks or anything. On the ACB panel there are 4 LED lights in a column, top light was off when I took panel off. Switched to emergency back up, all lights went out. When i switched back, top LED light was out others came on. There is a small panel with red LED writing which says 'ON' to the left of it are 2 red lines.
to MK Group Ltd - I assume we have 230 v but don't know how to check, i am in no way an engineer of any sort! Not sure waht you mean by "and the CH Pump?".
This is so frustrating as it could be something so simple and i may end up paying loads of money for a 5 min job! Done this before, charged a £100 by a 'Gledhill Specialist' who didn't even fix it. He charged me for all the phone calls he made to the Gledhill company, guess I was naive, shouldn't have paid.
Mimatron- Posts : 14
Join date : 2011-10-24
Re: No heating
Here is manual for the system:
http://www.aroundtownflats.com/manuals/Boilers/Gledhill/boilermatemain%205.pdf
Page 35 says how to check temperature and errors.
Page 22: 220V should be between pins 12-13 for pump and 27-28 for thermostat. You need to use multimeter for example to measure voltage(be careful). I would also check between 20-23 to make sure that timer is not faulty.
Page 28 explains LEDs.
If you have "switch" then your diagram is on Page 25 so for 220V pump need to measure on switch board between N-HTGpump
http://www.aroundtownflats.com/manuals/Boilers/Gledhill/boilermatemain%205.pdf
Page 35 says how to check temperature and errors.
Page 22: 220V should be between pins 12-13 for pump and 27-28 for thermostat. You need to use multimeter for example to measure voltage(be careful). I would also check between 20-23 to make sure that timer is not faulty.
Page 28 explains LEDs.
If you have "switch" then your diagram is on Page 25 so for 220V pump need to measure on switch board between N-HTGpump
scorp- Posts : 77
Join date : 2010-07-07
no heating
ah ha. LED display: Bar 1 - HT is lit, bar 2 - ST is lit, bar 3 - HW is out.
temps read as follows: store_T1 = 75, T1_ON = 74, T1_OFF= 77
PHE_T2=74, 69, 75
DHW_T3= HEr,
So all 3 green LED lights are working but the Bar 3 - HW isn't lit. So does that mean the pump in the IDEAL boiler isn't working and the Gledhill boiler is ok?
temps read as follows: store_T1 = 75, T1_ON = 74, T1_OFF= 77
PHE_T2=74, 69, 75
DHW_T3= HEr,
So all 3 green LED lights are working but the Bar 3 - HW isn't lit. So does that mean the pump in the IDEAL boiler isn't working and the Gledhill boiler is ok?
Mimatron- Posts : 14
Join date : 2011-10-24
no heating
Done the other bits but not going to test electrics, a step too far for me!
Mimatron- Posts : 14
Join date : 2011-10-24
Re: No heating
HW is hot water i think and it should be on when you open hot water tap
scorp- Posts : 77
Join date : 2010-07-07
Re: No heating
DHW_T3= HEr means sensor error. I think this is the answer to your problem
scorp- Posts : 77
Join date : 2010-07-07
no heating
So it means hot water pump has gone in IDEAL boiler? We will call someone out tomorrow. Thanks for all your help and patience.
Mimatron- Posts : 14
Join date : 2011-10-24
Re: No heating
No, boiler is fine I think. Your Store Temperature is 75 means that boiler works fine. I'm actually not sure how HW sensor can stop central heating working. I don't know how error checking works. Did you switch off system and switched on with jumper 5 for selftest as explained on page 35? The error may be left from previous selftest carried by someone who fixed sensor.
scorp- Posts : 77
Join date : 2010-07-07
No heating.
No I haven't tried the jumper 5 thing, will look at it again. Maybe I read it ut didn't get it, although i don't recall it. Will let you know. Thanks.
Mimatron- Posts : 14
Join date : 2011-10-24
no heating
I looked up jumper 5 on internet, i don't have one and can't do anything electical anyway.
Now have error showing on ST as well as HW even though red bar is showing on ST. This just gets more confusing.
Now have error showing on ST as well as HW even though red bar is showing on ST. This just gets more confusing.
Mimatron- Posts : 14
Join date : 2011-10-24
Re: No heating
Hi Mimatron
The answer to your problem is very simple to identify with the information that you have already supplied.
You have advised that out of the four green lights (LEDs) on the Boilermates control board, the bottom three are lit up. This confirms the following to me;
1] the boiler is being told to produce heat (fire up the burner)
2] the boiler pump is being told to work (this pumps the heated water from the boiler to the Boilermate)
3] the central heating boiler is being told to work
If the central heating pump is being told to work by the control board, but your radiators are still cold, then either the central heating pump itself is faulty or there is a problem with the control board in the Boilermate. Either way you will need to call a Gledhill specialist to rectify the situation. Please DO NOT proceed with trying any tests to establish if you have voltages unless you have electrical training as you may well put yourself in danger.
Our company covers the Midlands area, but if you are outside of our area then check the engineers section of this website for a more local specialist.
David HIckey
The answer to your problem is very simple to identify with the information that you have already supplied.
You have advised that out of the four green lights (LEDs) on the Boilermates control board, the bottom three are lit up. This confirms the following to me;
1] the boiler is being told to produce heat (fire up the burner)
2] the boiler pump is being told to work (this pumps the heated water from the boiler to the Boilermate)
3] the central heating boiler is being told to work
If the central heating pump is being told to work by the control board, but your radiators are still cold, then either the central heating pump itself is faulty or there is a problem with the control board in the Boilermate. Either way you will need to call a Gledhill specialist to rectify the situation. Please DO NOT proceed with trying any tests to establish if you have voltages unless you have electrical training as you may well put yourself in danger.
Our company covers the Midlands area, but if you are outside of our area then check the engineers section of this website for a more local specialist.
David HIckey
No heating
Thank you david, I did call an engineer who was familiar with the GLEDHILL sysyem he put in a new pump and now the water is getting to the radiators and we have a warm house! I would NEVER mess with electrics.
Mimatron- Posts : 14
Join date : 2011-10-24
Page 1 of 2 • 1, 2
Similar topics
» Please HELP !!! No heating
» central heating on when water heating up?
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
» No Heating
» H/W but no Heating
» central heating on when water heating up?
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
» No Heating
» H/W but no Heating
Page 1 of 2
Permissions in this forum:
You cannot reply to topics in this forum
|
|