Cycling Boiler
I have a systemate III and teh boiler keeps cycling even thougth the temp on the store seems to be hot enough. It cycles on for a few seconds. Goes off then about 30 seconds later will cycle again this happens a lot.
The readings from the lcd are
On - off - store - phe - dhw if that is correct i have taken these readings when its cycling
66 - 69 - 68 - 60 - 64
67 - 70 - 65 - 61 - 64
67 - 70 - 71 - 62 - 66
68 - 71 - 70 - 60 - 65
65 - 68 - 70 - 63 - 66
Could this be to do with the pump not circulating the water.
James
The readings from the lcd are
On - off - store - phe - dhw if that is correct i have taken these readings when its cycling
66 - 69 - 68 - 60 - 64
67 - 70 - 65 - 61 - 64
67 - 70 - 71 - 62 - 66
68 - 71 - 70 - 60 - 65
65 - 68 - 70 - 63 - 66
Could this be to do with the pump not circulating the water.
James
jaycee- Posts : 6
Join date : 2009-06-13
Re: Cycling Boiler
Hi Jaycee,
Yes if the boiler is firing for such a short time this indicates low water flow rate through the boiler. This could be the pump not running. Could be jammed or it could be a control board logic error/failure.
Cheers, Mike
Yes if the boiler is firing for such a short time this indicates low water flow rate through the boiler. This could be the pump not running. Could be jammed or it could be a control board logic error/failure.
Cheers, Mike
Cycling boiler
Do you mean pump circuit board or systemate iii board ?
The Pump seems to be running at same speed whichever setting it is on 1 2 or 3 so looks like pump issue.
The Pump seems to be running at same speed whichever setting it is on 1 2 or 3 so looks like pump issue.
jaycee- Posts : 6
Join date : 2009-06-13
Re: Cycling Boiler
I meant the control board in the III.
The pump running at the same speed whatever the speed setting suggests something else though. The pump has no water in it! The 'no load speed' on a pump is approximately the same whatever the speed setting. Once filled with water and purged of air the speed will vary when the speed setting is changed.
Cheers, Mike
The pump running at the same speed whatever the speed setting suggests something else though. The pump has no water in it! The 'no load speed' on a pump is approximately the same whatever the speed setting. Once filled with water and purged of air the speed will vary when the speed setting is changed.
Cheers, Mike
Similar topics
» The boiler starts up and starts cycling while boilermate control board status shows pump and boiler off
» boiler mate 2 hot water pump runs a lot, boiler not staying on long enough
» boiler mate 11 and ideal classic boiler firing three or four times
» Variable voltage to boiler from tank PCB: Boiler not firing
» SysteMate 2000 - Constantly Boiling/Cycling
» boiler mate 2 hot water pump runs a lot, boiler not staying on long enough
» boiler mate 11 and ideal classic boiler firing three or four times
» Variable voltage to boiler from tank PCB: Boiler not firing
» SysteMate 2000 - Constantly Boiling/Cycling