Hello,
As of saturday morning my Central Heating fuse tripped causing the Electramate 2000 (do not know if its the 9 & 12 model) to completely power down.
So from Sat morning I have had no hot water just tepid if that.
My central heating switch had tripped off which caused that the Electramate to power off, I
flipped it back on and the Electramate turned back on again but since
that I'm unable to get hot water.
I'm not very DIY savy but I have tried to go through the forums and
the instruction manual but my inexperience with these matters I cannot
completley say if I have a faulty part etc.
My ACB readings are
T1 - 28
Phe_T2 - 27
DHW_T3 - 25
I understand they are very low ....
I cant believe categorically the Electramate powering down and powering back on would cause part failure\s on the Electramate when i have not had a problem with it at all before that.
Any assistance would be gratefully recieved :-)
Thank you
As of saturday morning my Central Heating fuse tripped causing the Electramate 2000 (do not know if its the 9 & 12 model) to completely power down.
So from Sat morning I have had no hot water just tepid if that.
My central heating switch had tripped off which caused that the Electramate to power off, I
flipped it back on and the Electramate turned back on again but since
that I'm unable to get hot water.
I'm not very DIY savy but I have tried to go through the forums and
the instruction manual but my inexperience with these matters I cannot
completley say if I have a faulty part etc.
My ACB readings are
T1 - 28
Phe_T2 - 27
DHW_T3 - 25
I understand they are very low ....
I cant believe categorically the Electramate powering down and powering back on would cause part failure\s on the Electramate when i have not had a problem with it at all before that.
Any assistance would be gratefully recieved :-)
Thank you
Sash- Posts : 6
Join date : 2012-01-01
Re: No Heating or Hot Water Electrmate2000
Have you any green led's on the ACB lit up?
Page 31 of the manual section 3.4 have you done that?
After that has the boiler stat tripped?
Have you any errors when going through the ACB check?
There are none of these units in my area and thus I have never dealt with them.
Is the unit heating up?
Mike
MGC/H2O
Norfolk
Page 31 of the manual section 3.4 have you done that?
After that has the boiler stat tripped?
Have you any errors when going through the ACB check?
There are none of these units in my area and thus I have never dealt with them.
Is the unit heating up?
Mike
MGC/H2O
Norfolk
Fault Finding
Hello Mike,
LED Lights on the Board that are lit are HL1 & HL2 .
Followed correctly the functional tests, switched off mains, added jumper 5 and switched back on again. It carried out all of its tests successfully. Switched mains back off and removed jumper 5 & turned back on again.
To my knowledge the overheat thermostat has not tripped, I cannot see it pushed out like the manual suggests.
Running the ACB check provides no errors ....
Currently the readings are T1-25
phe_T2 - 23
dhw_T3 - 22
Thank you in advance
LED Lights on the Board that are lit are HL1 & HL2 .
Followed correctly the functional tests, switched off mains, added jumper 5 and switched back on again. It carried out all of its tests successfully. Switched mains back off and removed jumper 5 & turned back on again.
To my knowledge the overheat thermostat has not tripped, I cannot see it pushed out like the manual suggests.
Running the ACB check provides no errors ....
Currently the readings are T1-25
phe_T2 - 23
dhw_T3 - 22
Thank you in advance
Sash- Posts : 6
Join date : 2012-01-01
Re: No Heating or Hot Water Electrmate2000
So LED 1 & 2 are lit, suggesting it is heating?
Can you hear it heating?
Mike
MGC/H2O
Norfolk
Can you hear it heating?
Mike
MGC/H2O
Norfolk
Fault Finding
Hello Mike,
Through the course of further investigation and checking wiring etc, the Electramate started working successfully again. I will be buying a replacment 25 a HRC fuse. We checked the pumps etc, all of it seemed to be heating correctly.
I increased the temp on the Danflos Thermostat and that kicked in the entire unit successfully, after some time for the hot water it was working sufficiently again.
I have been monitoring the reading since then and it seems ok.
I had a brief few minutes where the unit was very loud but i think that was more trapped air which did stop after the hot tap was started.
Thank you for taking an interest in my issue.
Through the course of further investigation and checking wiring etc, the Electramate started working successfully again. I will be buying a replacment 25 a HRC fuse. We checked the pumps etc, all of it seemed to be heating correctly.
I increased the temp on the Danflos Thermostat and that kicked in the entire unit successfully, after some time for the hot water it was working sufficiently again.
I have been monitoring the reading since then and it seems ok.
I had a brief few minutes where the unit was very loud but i think that was more trapped air which did stop after the hot tap was started.
Thank you for taking an interest in my issue.
Sash- Posts : 6
Join date : 2012-01-01
Similar topics
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
» no hot water, but heating ok
» No hot water or heating
» Heating but no hot water
» Hot water but no heating
» no hot water, but heating ok
» No hot water or heating
» Heating but no hot water
» Hot water but no heating
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum