If I turn my boilermate 2000 off, leave it unpowered for a while and then turn it back on, all is well for a while but as soon as I draw hot water the central heating comes on full blast and stays on regardless of the clock or thermostat setting. I suspect the control board is kaput especially as the LCD is completely blank whatever button I press. It looks fairly straightforward to put a new one in but I am reluctant to do so unless I'm sure it fixes the problem (the ACB seems a tad pricey), so to put my mind a rest a little I wonder if someone could answer a couple of questions:
Do the boards just break, or is there likely to be some external problem that should be checked out first.
What do the jumper settings do, the manual says use positions 1, 3 & 4 but my boilermate has only position 4 and must have been like that since new 8+ years ago.
The board has four LED (one per pump plus one not used), all of mine are lit all the time, even the 'not used' LED. Is this normal?
Anything else I should be concerned with?
Many thanks for any help ...
James
Do the boards just break, or is there likely to be some external problem that should be checked out first.
What do the jumper settings do, the manual says use positions 1, 3 & 4 but my boilermate has only position 4 and must have been like that since new 8+ years ago.
The board has four LED (one per pump plus one not used), all of mine are lit all the time, even the 'not used' LED. Is this normal?
Anything else I should be concerned with?
Many thanks for any help ...
James
JamesKemp- Posts : 1
Join date : 2012-07-13
Re: Continuous heating = dead ACB?
Jumper settings are very important.
Your PCB has gone.
Power surges / lightening are the main causes.
DO NOT TOUCH THE NEW PCB use gloves or what have you.
Mike
MGC/H2O
Norfolk
Your PCB has gone.
Power surges / lightening are the main causes.
DO NOT TOUCH THE NEW PCB use gloves or what have you.
Mike
MGC/H2O
Norfolk
Re: Continuous heating = dead ACB?
James,
It reminds me the situation with old Sky boxes when you have them on for years then decided to change some wiring's unplugging box from mains. After that box doesn't start. It is electrolytic capacitors issue. Check my answer here how to fix it: https://gledhill-repairs.forumotion.net/t957-boilermate-2000-ignores-store-satisfied-temp-t1_off#3035
I had nearly the same problem: https://gledhill-repairs.forumotion.net/t969-pcb-fault-fixing
Unless correct jumpers fix the problem(but I suspect you had working unit with the same settings for years and didn't touch jumpers)
It reminds me the situation with old Sky boxes when you have them on for years then decided to change some wiring's unplugging box from mains. After that box doesn't start. It is electrolytic capacitors issue. Check my answer here how to fix it: https://gledhill-repairs.forumotion.net/t957-boilermate-2000-ignores-store-satisfied-temp-t1_off#3035
I had nearly the same problem: https://gledhill-repairs.forumotion.net/t969-pcb-fault-fixing
Unless correct jumpers fix the problem(but I suspect you had working unit with the same settings for years and didn't touch jumpers)
scorp- Posts : 77
Join date : 2010-07-07
Re: Continuous heating = dead ACB?
scorp wrote:James,
It reminds me the situation with old Sky boxes when you have them on for years then decided to change some wiring's unplugging box from mains. After that box doesn't start. It is electrolytic capacitors issue. Check my answer here how to fix it: https://gledhill-repairs.forumotion.net/t957-boilermate-2000-ignores-store-satisfied-temp-t1_off#3035
I had nearly the same problem: https://gledhill-repairs.forumotion.net/t969-pcb-fault-fixing
Unless correct jumpers fix the problem(but I suspect you had working unit with the same settings for years and didn't touch jumpers)
Hi Scorp,
Where can you get these capacitors from ?
Sounds like they could be a possible solution to my issue
RichB14- Posts : 8
Join date : 2012-06-21
Re: Continuous heating = dead ACB?
Here it is(don't pay attention on the values on the pictures):
220uF x 25V
10uF x 50V
47uF x 50V
or from Maplin
220uF x 25V
10uF x 50V
47uF x 50V
or from Maplin
scorp- Posts : 77
Join date : 2010-07-07
Re: Continuous heating = dead ACB?
Excellent, i'll get some ordered up
RichB14- Posts : 8
Join date : 2012-06-21
RS Part numbers
Thanks for the advice I've replaced the caps and now have both a working spare and one on the boilermate.
I ordered parts from RS and got five of each capacitor for a total bill of around £4. The part numbers are:
3150552 220 microF
3654240 10 microF
572198 47 microF
Not bad eh, £400 worth of boards fixed for £4!
I ordered parts from RS and got five of each capacitor for a total bill of around £4. The part numbers are:
3150552 220 microF
3654240 10 microF
572198 47 microF
Not bad eh, £400 worth of boards fixed for £4!
RichardJ- Posts : 1
Join date : 2012-10-26
Re: Continuous heating = dead ACB?
Richard,RichardJ wrote:Thanks for the advice I've replaced the caps and now have both a working spare and one on the boilermate.
I ordered parts from RS and got five of each capacitor for a total bill of around £4. The part numbers are:
3150552 220 microF
3654240 10 microF
572198 47 microF
Not bad eh, £400 worth of boards fixed for £4!
That is really good news. Glad that my advice helped someone
scorp- Posts : 77
Join date : 2010-07-07
Re: Continuous heating = dead ACB?
I seem to be having similar problems with my Boilermate 2000 where my heating started coming on at random times.....
I checked the ACB, all 3 pump LED's were constantly on and the digit readout was "ON.". I turned the power off and left for a few mins but the digit readout now doesn't come on and pressing the buttons does nothing. The 3 pump LED's still on. Also, the heating now seems to be permanently!
Order now placed with RS so hopefully this will be a cheep fix.
One other thing that's not related was that I noticed was that my GlowWorm boiler's thermostat was not set to max. Is this something I should change as the manual says the boiler should be set to max?
Nige_S- Posts : 1
Join date : 2014-04-27
Re: Continuous heating = dead ACB?
Main ACB has failed.
And YES
The boiler stat needs to be on max.
As the BM 2000 will tell it when it is happy.
Oh and you use more gas having it on lower.
Mike
And YES
The boiler stat needs to be on max.
As the BM 2000 will tell it when it is happy.
Oh and you use more gas having it on lower.
Mike
Re: Continuous heating = dead ACB?
Another processor brought back to life by changing 5 caps. Thanks
Weeguy- Posts : 4
Join date : 2017-07-23
Re: Continuous heating = dead ACB?
I'm glad it helped people save some money :). My boiler has been working for 7 years since I fixed it by changing caps.Weeguy wrote:Another processor brought back to life by changing 5 caps. Thanks
scorp- Posts : 77
Join date : 2010-07-07
Re: Continuous heating = dead ACB?
The caps worked for me too, it's a 16 year old controller that now works again and doesn't give undemanded heating. Thank you, particularly for the part numbers.
m_costelloe- Posts : 2
Join date : 2017-09-17
Re: Continuous heating = dead ACB?
Hi all,
I have the same problem outlined above (heating stuck on despite timer and thermostat set to off).
Is changing the caps straight forward? Is there anyone that has done it that could provide a quick guide please?
Really want to avoid having to drop hundreds on a repair with everything going on at the moment!
Thank you
I have the same problem outlined above (heating stuck on despite timer and thermostat set to off).
Is changing the caps straight forward? Is there anyone that has done it that could provide a quick guide please?
Really want to avoid having to drop hundreds on a repair with everything going on at the moment!
Thank you
Thornton2020- Posts : 1
Join date : 2020-10-28
ACB repair
I can repair the acb for you I also offer a reconditioned ACB exchange so you get a solution as quickly as possible. Have a look at my website for more details: https://murraymartin.yolasite.com/purchase-page.php
repair £45 exchange or £100 for reconditioned pcb with £45 refund for the faulty board when returned to me.
Unless you have some experience and the correct equipment trying to repair these pcb's can result in the pcb being damaged quite badly. Regards Murray
repair £45 exchange or £100 for reconditioned pcb with £45 refund for the faulty board when returned to me.
Unless you have some experience and the correct equipment trying to repair these pcb's can result in the pcb being damaged quite badly. Regards Murray
Similar topics
» PCB Dead? Hot water/No Heating Engineer wants £2500
» central heating on when water heating up?
» Boilermate 2000 no switch function
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
» PULSACOIL 2000 NO HOT WATER LED PSC LIGHT CONTINUOUS FLASHING
» central heating on when water heating up?
» Boilermate 2000 no switch function
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
» PULSACOIL 2000 NO HOT WATER LED PSC LIGHT CONTINUOUS FLASHING
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum