Boilermate SP Bypass Valve Leaking

View previous topic View next topic Go down

Boilermate SP Bypass Valve Leaking

Post  chrismoody on Fri Feb 22, 2013 5:21 am

Hi

The Bypass valve on my Boilermate SP is Leaking from the red plastic end.

Is this something that can be repaired or do I have to replace it. If I tighten it the leak lessens but does not stop.

Is it something you would recommend doing yourself.

Money is tight so replacing it myself is an appealing option.

Thanks for any advice you can offer.

chrismoody

Posts : 1
Join date : 2013-02-22

View user profile

Back to top Go down

Re: Boilermate SP Bypass Valve Leaking

Post  Mario.S on Fri Feb 22, 2013 4:33 pm

this valve is a 3 bar over pressure release valve ( for your safety) , so no repair, fit a new one. also have a close look at your expansion vessel, 1 bar air pressure required, ( testing only with the system pressure on zero!!!!)
regards Mario at Mario's Boiler Service