No Hot Water & No CH
2 posters
Page 1 of 1
No Hot Water & No CH
Hi There wondered if anyone could advise
System is firing up, hot water going into tank three green lights on but only one pump running, CH and DHW not running. Red Light says ON but only one bar showing (Middle One) Removed PCB and it appeared OK, reinstated it and let it go through its start up, three green lights on and two bars, still only one pump running, Checked other two pumps and they are not running, removed screw in middle to prove etc.
Is it the pcb ?
System is firing up, hot water going into tank three green lights on but only one pump running, CH and DHW not running. Red Light says ON but only one bar showing (Middle One) Removed PCB and it appeared OK, reinstated it and let it go through its start up, three green lights on and two bars, still only one pump running, Checked other two pumps and they are not running, removed screw in middle to prove etc.
Is it the pcb ?
skippa- Posts : 7
Join date : 2012-08-31
Re: No Hot Water & No CH
The boiler pump is running?
Heating pump will only run if timer on and room stat calling.
AND only if the unit is 60c or higher!
The DHW pump will only run if a hot tap is on.
Sometimes it is best to check if there is a voltage at the pump. Along with big screw out and finger in the hole etc.
It has been know for the impeller to become detached from the pump to.
Is the unit full?
Check by draining some out and see if it takes water from the F & E tank.
If it does not then the internal cold feed is blocked.
If still in doubt check and carry out as per the book / commissioning the unit.
It is usual when a PCB /ACB to go that the heating will run and not stop/
Or the display is blank. But this does vary.
Have you had a storm recently? This will take the PCB's out too.
All the sensors / everything is / are controlled by the ACB so it is pointing that way.
If you really want to try a bit harder.
Make sure the unit is hot.
Remove cable from middle / heating pump and make safe.
Connect a temporary lead via an extension lead / plug and see if the heating works.
But be very careful when adding an extra supply into the equation. You have been WARNED !
Try the above and check.
Report back.
Mike
MGC/H2O
Norfolk
Heating pump will only run if timer on and room stat calling.
AND only if the unit is 60c or higher!
The DHW pump will only run if a hot tap is on.
Sometimes it is best to check if there is a voltage at the pump. Along with big screw out and finger in the hole etc.
It has been know for the impeller to become detached from the pump to.
Is the unit full?
Check by draining some out and see if it takes water from the F & E tank.
If it does not then the internal cold feed is blocked.
If still in doubt check and carry out as per the book / commissioning the unit.
It is usual when a PCB /ACB to go that the heating will run and not stop/
Or the display is blank. But this does vary.
Have you had a storm recently? This will take the PCB's out too.
All the sensors / everything is / are controlled by the ACB so it is pointing that way.
If you really want to try a bit harder.
Make sure the unit is hot.
Remove cable from middle / heating pump and make safe.
Connect a temporary lead via an extension lead / plug and see if the heating works.
But be very careful when adding an extra supply into the equation. You have been WARNED !
Try the above and check.
Report back.
Mike
MGC/H2O
Norfolk
update
Thanks for the reply Mike.
Looking at the boiler the three pumps, the one on the right is running constantly. I hard wired the ther two to prove they operated OK.
When I switch on three green lights appear it does its setting up then the On light comes on with the middle red bar. When I operate room stat nothing happens. Room stat is working I checked signal to PC.
We did recently have storms,checked header tank this was OK.
I even changed link 4 to 5 nothing happened
Not getting any ERR codes and can not operate SW1 or SW2.
I suspect the PCB so I have ordered one
Will update when it arrives thanks for the help
Looking at the boiler the three pumps, the one on the right is running constantly. I hard wired the ther two to prove they operated OK.
When I switch on three green lights appear it does its setting up then the On light comes on with the middle red bar. When I operate room stat nothing happens. Room stat is working I checked signal to PC.
We did recently have storms,checked header tank this was OK.
I even changed link 4 to 5 nothing happened
Not getting any ERR codes and can not operate SW1 or SW2.
I suspect the PCB so I have ordered one
Will update when it arrives thanks for the help
skippa- Posts : 7
Join date : 2012-08-31
pcb arrived
Hi Mike. PCB arrived today. Put links on 1,3 and 4. Nothing much happened for ages. Middle red bar was on and little flashing light in corner of display. Also a permanent red light just below display. The boiler is not kicking in. Put link from 4 to 5 and it made the boiler kick in. And one green light. It now says ON with two bars above it. The green light is for the Boiler On. When I put the link back from 5 to 4 it just locks up Is there a time period for the self commission ?
skippa- Posts : 7
Join date : 2012-08-31
Re: No Hot Water & No CH
1,3 & 4
But to commission you need to switch off link on 5
Go through test etc.
Switch off remove 5
Job done
Mike
But to commission you need to switch off link on 5
Go through test etc.
Switch off remove 5
Job done
Mike
Gulfstream 2000
Hi Mike. Thanks again for the reply. Was sent PCB for a Gulfstream 2000. This I believe can not bne used on a Boilermate 2000 . Steve
skippa- Posts : 7
Join date : 2012-08-31
confused
Evening Mike. I put the unit on buit would only ignite boiler when Link 5 in. Lookled on installation manual and it said the Boilermate 2000 required a. V29 chip and the Gulfstream. Used a V40 chip ?
skippa- Posts : 7
Join date : 2012-08-31
Re: No Hot Water & No CH
Well all the ACB's I have fitted for the 2000.
Are used for others too.
Hence the jumpers.
But there is conflict with parts numbers in the books
In my Gledhill spares book.
Etc etc.
Where did you get the board?
Are used for others too.
Hence the jumpers.
But there is conflict with parts numbers in the books
In my Gledhill spares book.
Etc etc.
Where did you get the board?
Re: No Hot Water & No CH
UK Heating Spares in Preston. Bought it on EBay shop
skippa- Posts : 7
Join date : 2012-08-31
Re: No Hot Water & No CH
Thanks for that Mike. Hopefully they will change it !
skippa- Posts : 7
Join date : 2012-08-31
Similar topics
» Pulsacoil 2000 -Hot water in the thermal store but cold water from the taps.
» Only short blasts of hot water in the morning, rarely hot water in the afternoon/evening
» No hot water, red fault light on, after adjusting thermostat
» Gledhill Boilermate Class A OV - PHE (hot water) pump constantly whirring, but no hot water
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
» Only short blasts of hot water in the morning, rarely hot water in the afternoon/evening
» No hot water, red fault light on, after adjusting thermostat
» Gledhill Boilermate Class A OV - PHE (hot water) pump constantly whirring, but no hot water
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.