Boilermate2000, heating on when both thermostat and timer switched off!
2 posters
Page 1 of 1
Boilermate2000, heating on when both thermostat and timer switched off!
Hi, my heating is on constantly despite the wall thermostat being turned right down and the timer on the boilermate being switched off. System is 7 years old and PCB was renewed 2 years ago ! Have switched everything off and back on again but no luck resetting. Surely not another PCB ..... Any advice appreciated. Thanks
Val22- Posts : 4
Join date : 2012-10-14
Re: Boilermate2000, heating on when both thermostat and timer switched off!
Look at the PCB display.
But it does sound like the PCB
Lightening strikes in and around your area can take them out
And power surges from the mains supply.
You had any other things go wrong?
What about neighbours?
Mike
MGC/H2O
Norfolk
PS;
I fit loads of them!
But it does sound like the PCB
Lightening strikes in and around your area can take them out
And power surges from the mains supply.
You had any other things go wrong?
What about neighbours?
Mike
MGC/H2O
Norfolk
PS;
I fit loads of them!
Re: Boilermate2000, heating on when both thermostat and timer switched off!
Thanks Mike, we had a power surge last week and this happened 2-3days later. Neighbours that I spoke to are all fine. Actually met the couple I bought house from and they have had PCB renewed as well before I moved in, so this could be no.3 .....
Val22- Posts : 4
Join date : 2012-10-14
Re: Boilermate2000, heating on when both thermostat and timer switched off!
Well you need to look at surge / spike protection!
Mike
Mike
Re: Boilermate2000, heating on when both thermostat and timer switched off!
Thanks Mike, switched off completely as was away for a weeks holiday, now back and had an electrician out to look at surge / spike as per your recommendation. Everything all ok and Circuit Breaker in place.
Whilst here, he took the front off the boilermate and had a look ..... PCB not showing anything on the display.
Guess its back to British Gas to have PCB replaced for third time.
For info ..... how much would it cost to buy new PCB directly ?
Thanks again, much appreciated.
Val
Whilst here, he took the front off the boilermate and had a look ..... PCB not showing anything on the display.
Guess its back to British Gas to have PCB replaced for third time.
For info ..... how much would it cost to buy new PCB directly ?
Thanks again, much appreciated.
Val
Val22- Posts : 4
Join date : 2012-10-14
Re: Boilermate2000, heating on when both thermostat and timer switched off!
BM 2000 Main board from
South Coast Green Energies £255:00p
Mike
South Coast Green Energies £255:00p
Mike
Re: Boilermate2000, heating on when both thermostat and timer switched off!
And ref Surge / spike protection.
That would be an add on to prevent the same happening in the future!
Mike
That would be an add on to prevent the same happening in the future!
Mike
Re: Boilermate2000, heating on when both thermostat and timer switched off!
Mike, once again many thanks. Greatly Appreciated.
Val22- Posts : 4
Join date : 2012-10-14
Similar topics
» Heating does not come on on the timer - have replaced timer to no avail
» Heating timer controls not working.
» Help - Heating does not switch off (Ideal boiler - BoilerMate2000)
» No heating when on timer mode
» No hot water/heating but thermostat says it is on
» Heating timer controls not working.
» Help - Heating does not switch off (Ideal boiler - BoilerMate2000)
» No heating when on timer mode
» No hot water/heating but thermostat says it is on
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum