Hi there,
Wondering if anyone could help me with their experience?
I have switched off the heating completely (off on the Thermostat / Remote Controller) and I have left all the radiators turned off (no water going to it) apart from one in the hallway and when I woke up yesterday morning, it was warm to touch, so I did a little experiment, turned that off and turned the one in my room on - same thing, it was warm to touch.
Is it normal for the radiator to be warm (very tepid) to touch when the heating is switched off?
Many Thanks
Wondering if anyone could help me with their experience?
I have switched off the heating completely (off on the Thermostat / Remote Controller) and I have left all the radiators turned off (no water going to it) apart from one in the hallway and when I woke up yesterday morning, it was warm to touch, so I did a little experiment, turned that off and turned the one in my room on - same thing, it was warm to touch.
Is it normal for the radiator to be warm (very tepid) to touch when the heating is switched off?
Many Thanks
9000se- Posts : 5
Join date : 2013-04-09
Re: Is it normal for the radiators to be warm?
You could have a problem.
But heat will travel etc.
Heat rises.
If it does it will move.
Mike
But heat will travel etc.
Heat rises.
If it does it will move.
Mike
Re: Is it normal for the radiators to be warm?
Hi
I know this reply is a bit late, but the radiators shouldn't get hot when the central heating is switched off on and Electramate unit.
Water has to be circulating to allow the radiators to heat up even a little bit, and with the heating turned off, the central heating pump doesn't run.
There are two possible causes for this. The most probable cause is that the non return valve below the central heating could be faulty, allowing water to pass to the radiators whenever the hot water pump is running (they are both on the same branch of pipework).
The other possibility, although extremely rare, is that the ACB circuit board is allowing a trickle voltage to the heating pump, and thus allowing the pump to run.
I would be inclined to replace the non return valve and retest the unit before I did anything else.
Hope this helps
I know this reply is a bit late, but the radiators shouldn't get hot when the central heating is switched off on and Electramate unit.
Water has to be circulating to allow the radiators to heat up even a little bit, and with the heating turned off, the central heating pump doesn't run.
There are two possible causes for this. The most probable cause is that the non return valve below the central heating could be faulty, allowing water to pass to the radiators whenever the hot water pump is running (they are both on the same branch of pipework).
The other possibility, although extremely rare, is that the ACB circuit board is allowing a trickle voltage to the heating pump, and thus allowing the pump to run.
I would be inclined to replace the non return valve and retest the unit before I did anything else.
Hope this helps