Low/no voltage at boiler and pump connections on PCB
3 posters
Page 1 of 1
Low/no voltage at boiler and pump connections on PCB
Hi Guys,
I've got a problem with a Boilermate 2000. My boiler and central heating pump appear not to operate when there is a demand for heat or hot water from the central heating programmer. Having got my multimeter out I have seen that the voltage to each component at the PCB is about 2v when there a demand from the programmer. The funny thing is that if I disconnect the wiring of the component at the board and measure the voltage then I get 230v.
Would I be right in thinking the PCB is at fault or should I be looking elsewhere? I would state that I've changed the PCB on the boiler thinking this was the issue. Each of the boiler components has been checked and work.
Yours,
Mark
I've got a problem with a Boilermate 2000. My boiler and central heating pump appear not to operate when there is a demand for heat or hot water from the central heating programmer. Having got my multimeter out I have seen that the voltage to each component at the PCB is about 2v when there a demand from the programmer. The funny thing is that if I disconnect the wiring of the component at the board and measure the voltage then I get 230v.
Would I be right in thinking the PCB is at fault or should I be looking elsewhere? I would state that I've changed the PCB on the boiler thinking this was the issue. Each of the boiler components has been checked and work.
Yours,
Mark
mark_r- Posts : 3
Join date : 2014-01-08
Re: Low/no voltage at boiler and pump connections on PCB
Can you read the red bar display?
Can you read through the fault codes?
Mike
Can you read through the fault codes?
Mike
Re: Low/no voltage at boiler and pump connections on PCB
Hi Mike, do you mean the LEDs when you say the red bar display? If so all LEDs are lit when the fault occurs. Excuse my ignorance.
mark_r- Posts : 3
Join date : 2014-01-08
Re: Low/no voltage at boiler and pump connections on PCB
Right well try and go through the fault codes as per the book or instructions perhaps on inside the front cover.
Mike
Mike
Re: Low/no voltage at boiler and pump connections on PCB
Morning Mike,
Thanks for the advice, this is what I have so far.
As per the instructions I turn the BM2000 off at the supply and set it to boiler mode, set the heating system room stat to full and then turn on the electrical supply to the BM2000. There is nothing shown on the display, 4 green LEDs are all lit at the bottom. These LEDs are lit regardless of their being a demand for heat/hot water at the programmer or not. If I disconnect the wiring to the heating pump or boiler I get 213V at the terminals, if connected to the components this drops to about 1V. The incoming voltage is @40V.
When switched to the emergency functions the display does not come on either. The relevant pumps run though. Interestingly I'm only getting tepid hot water and no heat when set to emergency mode, I've measured 240V at the heating element when the emergency function is set. Could this mean I have an additional issue.
Prior to moving in 3 weeks ago the house had been empty for 6 months so I'm not sure of the background to the system.
Let me know if you need more info.
Mark
Thanks for the advice, this is what I have so far.
As per the instructions I turn the BM2000 off at the supply and set it to boiler mode, set the heating system room stat to full and then turn on the electrical supply to the BM2000. There is nothing shown on the display, 4 green LEDs are all lit at the bottom. These LEDs are lit regardless of their being a demand for heat/hot water at the programmer or not. If I disconnect the wiring to the heating pump or boiler I get 213V at the terminals, if connected to the components this drops to about 1V. The incoming voltage is @40V.
When switched to the emergency functions the display does not come on either. The relevant pumps run though. Interestingly I'm only getting tepid hot water and no heat when set to emergency mode, I've measured 240V at the heating element when the emergency function is set. Could this mean I have an additional issue.
Prior to moving in 3 weeks ago the house had been empty for 6 months so I'm not sure of the background to the system.
Let me know if you need more info.
Mark
mark_r- Posts : 3
Join date : 2014-01-08
Re: Low/no voltage at boiler and pump connections on PCB
I would check does the unit take water.
Hose on unit and drain, see if water level goes down in F & E tank.
Also use both drain off's.
Heater problem, are the fuses in? or mcb's on?
If you have no red bars on the display, then the main board has failed.
Remember you will NOT get any heating if the unit temperature drops below 60c.
Mike
Hose on unit and drain, see if water level goes down in F & E tank.
Also use both drain off's.
Heater problem, are the fuses in? or mcb's on?
If you have no red bars on the display, then the main board has failed.
Remember you will NOT get any heating if the unit temperature drops below 60c.
Mike
Re: Low/no voltage at boiler and pump connections on PCB
Sorry for the late replaymark_r wrote:Morning Mike,
Thanks for the advice, this is what I have so far.
As per the instructions I turn the BM2000 off at the supply and set it to boiler mode, set the heating system room stat to full and then turn on the electrical supply to the BM2000. There is nothing shown on the display, 4 green LEDs are all lit at the bottom. These LEDs are lit regardless of their being a demand for heat/hot water at the programmer or not. If I disconnect the wiring to the heating pump or boiler I get 213V at the terminals, if connected to the components this drops to about 1V. The incoming voltage is @40V.
When switched to the emergency functions the display does not come on either. The relevant pumps run though. Interestingly I'm only getting tepid hot water and no heat when set to emergency mode, I've measured 240V at the heating element when the emergency function is set. Could this mean I have an additional issue.
Prior to moving in 3 weeks ago the house had been empty for 6 months so I'm not sure of the background to the system.
Let me know if you need more info.
Mark
This sounds very likely , you need a new pcb. If no display showing on the pcb and all your neon are on, the processor on the pcb is crashed. The part is a GT155 Gledhill PCB.
also as Mike mentioned, check water contended in F&E tank, overflow and filling valves .
If your Boilermate has the Switch - electric backup system, you could use this temporarily, till you have the new GT155 PCB.
Hope this helps and happy new year Mario at Mario's Boiler Service
Similar topics
» Boiler and boiler pump not stopping
» Boiler pump running constantly
» Boiler pump keeps failing
» boiler mate 2 hot water pump runs a lot, boiler not staying on long enough
» Think Boiler Pump has died
» Boiler pump running constantly
» Boiler pump keeps failing
» boiler mate 2 hot water pump runs a lot, boiler not staying on long enough
» Think Boiler Pump has died
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum