Boilermate 2000 Store Temp
Hi All,
I've got a Boilermate 2000 (BM185) connected to a Potterton Suprima 60 in the town house I live in. The boiler is located on the ground floor, and the BM is located on the 2nd floor in an airing cupboard. There are 12 radiators of various sizes attached to the system. The F&E tank is in the loft directly above the BM.
The unit was installed in 2002 when the house was built. Since we moved into the house just over 2 years ago we've had numerous issues with it, mainly due to previous owners not maintaining anything in the house properly. The result was new sensors being fitted to the BM. However, the bigger issues were resolved by fitting a new control board to the Suprima about a year ago. This was despite BG saying there was nothing wrong with the old board as it was the latest revision. Yet when the finally changed it the hassle we had of the boiler going into lockout went away and we finally got a reliable system.
For the most part the system is fine, however reading on these forums it seems my store temperature doesn't get as hot as it should. During normal running the store temp sits at 69C. The Call temp is set around 62C and Satisfied is 69C. If the system is powered off these values get set higher (77/74), but after a few minutes of running the BM adjusts them down to 69/62.
I asked the BG engineer about this when he came to fit the circuit board to the Suprima and said it was because the boiler couldn't supply the water at the temperature the BM was requesting, so the BM adjusts down to values the boiler can supply. He also commented that it didn't help with the boiler being two floors beneath the BM and it was a fairly long pipe run. The pipe run to the boiler is probably about 4 metres, maybe a bit more.
I took a look at the times it took to heat the store this morning and the times were as follows:
65 > 66 : 1m16s
66 > 67 : 45s
67 > 68 : 48s
68 > 69 : 2m47s
As a result of the lower store temp we find that you can just about run one bath before we run out of hot water, and the central heating radiators do seem quite slow to get to temperature.
Would it be worth me attempting to drain the system down and refill it with some X400 for a while? Never fully drained it down, so obviously concerned about doing this. However, we've taken rads off for decorating, and when they've refilled we've observed the F&E tank refills as well, so I think that's ok.
Click on pic below to enlarge (quite surprised store temp managed to get to 70C in this pic)
Any advice would be appreciated. Let me know if more info is required.
Many Thanks...
I've got a Boilermate 2000 (BM185) connected to a Potterton Suprima 60 in the town house I live in. The boiler is located on the ground floor, and the BM is located on the 2nd floor in an airing cupboard. There are 12 radiators of various sizes attached to the system. The F&E tank is in the loft directly above the BM.
The unit was installed in 2002 when the house was built. Since we moved into the house just over 2 years ago we've had numerous issues with it, mainly due to previous owners not maintaining anything in the house properly. The result was new sensors being fitted to the BM. However, the bigger issues were resolved by fitting a new control board to the Suprima about a year ago. This was despite BG saying there was nothing wrong with the old board as it was the latest revision. Yet when the finally changed it the hassle we had of the boiler going into lockout went away and we finally got a reliable system.
For the most part the system is fine, however reading on these forums it seems my store temperature doesn't get as hot as it should. During normal running the store temp sits at 69C. The Call temp is set around 62C and Satisfied is 69C. If the system is powered off these values get set higher (77/74), but after a few minutes of running the BM adjusts them down to 69/62.
I asked the BG engineer about this when he came to fit the circuit board to the Suprima and said it was because the boiler couldn't supply the water at the temperature the BM was requesting, so the BM adjusts down to values the boiler can supply. He also commented that it didn't help with the boiler being two floors beneath the BM and it was a fairly long pipe run. The pipe run to the boiler is probably about 4 metres, maybe a bit more.
I took a look at the times it took to heat the store this morning and the times were as follows:
65 > 66 : 1m16s
66 > 67 : 45s
67 > 68 : 48s
68 > 69 : 2m47s
As a result of the lower store temp we find that you can just about run one bath before we run out of hot water, and the central heating radiators do seem quite slow to get to temperature.
Would it be worth me attempting to drain the system down and refill it with some X400 for a while? Never fully drained it down, so obviously concerned about doing this. However, we've taken rads off for decorating, and when they've refilled we've observed the F&E tank refills as well, so I think that's ok.
Click on pic below to enlarge (quite surprised store temp managed to get to 70C in this pic)
Any advice would be appreciated. Let me know if more info is required.
Many Thanks...
nimbus- Posts : 9
Join date : 2015-01-05
Location : Hertfordshire
Draining and cleaning a Boilermate 2000
Well looking at your picture, well done for that!
The flow from the boiler to the unit (left hand pipe) has quite a few bends!
Lots of bends / elbows mean resistance!
Yes it would be a good idea to drain some water from the unit.
Turn off water to F & E tank.
Drain until empty, then continue for at least another 5 to 10 minutes.
Stop draining.
Add at least 3 bottles of cleaner 4 would be better.
On draining and adding the cleaner you must bleed the pumps and any rads etc.
Then run the system.
Do not run the heating for a while.
By doing this the cleaner will concentrate on the boiler and pipe work to the BM 2000. And the BM 2000 too.
If the boiler stops running which it will once hot, run some hot water off and the boiler will fire again.
While the boiler and pump are running cleaner should be working.
Running the DHW will just go through the PHE.
If you can do the above and see any improvement great.
Then run the heating. But as it is cold you may have to use the heating.
Keep it in and watch the reading.
When the time comes or you are ready, the system will need draining in full.
The BM 2000.
The boiler and pipe work.
All the rads.
While draining you can let water into the F & E tank this will help flush out the system.
It is nice to drain until clear / clean water is seen.
After all this. Re fill the system and add at least 3 inhibitor but 4 would be better.
Bleed all the rads and pumps on BM 2000.
A lot of work and time, but can be worth it.
Mike
The flow from the boiler to the unit (left hand pipe) has quite a few bends!
Lots of bends / elbows mean resistance!
Yes it would be a good idea to drain some water from the unit.
Turn off water to F & E tank.
Drain until empty, then continue for at least another 5 to 10 minutes.
Stop draining.
Add at least 3 bottles of cleaner 4 would be better.
On draining and adding the cleaner you must bleed the pumps and any rads etc.
Then run the system.
Do not run the heating for a while.
By doing this the cleaner will concentrate on the boiler and pipe work to the BM 2000. And the BM 2000 too.
If the boiler stops running which it will once hot, run some hot water off and the boiler will fire again.
While the boiler and pump are running cleaner should be working.
Running the DHW will just go through the PHE.
If you can do the above and see any improvement great.
Then run the heating. But as it is cold you may have to use the heating.
Keep it in and watch the reading.
When the time comes or you are ready, the system will need draining in full.
The BM 2000.
The boiler and pipe work.
All the rads.
While draining you can let water into the F & E tank this will help flush out the system.
It is nice to drain until clear / clean water is seen.
After all this. Re fill the system and add at least 3 inhibitor but 4 would be better.
Bleed all the rads and pumps on BM 2000.
A lot of work and time, but can be worth it.
Mike
Re: Boilermate 2000 Store Temp
Many Thanks for the quick response and detailed instructions. Much appreciated.
For the cleaning product I was going to use 4 x X400 (1L), and for inhibitor 4 x X100 (1L). Are both recommended? If there's something better, let me know.
With regards to bleeding the pumps, is it just a case of loosening the screw on the front of each pump before turning the system on until water starts to dribble out? Or does a pump need to be running before it can be bled?
Cheers...
For the cleaning product I was going to use 4 x X400 (1L), and for inhibitor 4 x X100 (1L). Are both recommended? If there's something better, let me know.
With regards to bleeding the pumps, is it just a case of loosening the screw on the front of each pump before turning the system on until water starts to dribble out? Or does a pump need to be running before it can be bled?
Cheers...
nimbus- Posts : 9
Join date : 2015-01-05
Location : Hertfordshire
Re: Boilermate 2000 Store Temp
X400 & X100 are fine.
All bleeding really takes place before switching on.
But once on check again.
And when hot check again.
There may be a rad which collects air more than others.
Mike
All bleeding really takes place before switching on.
But once on check again.
And when hot check again.
There may be a rad which collects air more than others.
Mike
Similar topics
» Boilermate 2000 ignores store satisfied temp.. T1_OFF
» BoilerMate 2000 No hot water in the mornings when boiler turned on, HW pump runs continously when up to temp.
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
» Fitting Store Temp Sensor BM2000
» can i ajust the hot water temp on my 2000 plse ?
» BoilerMate 2000 No hot water in the mornings when boiler turned on, HW pump runs continously when up to temp.
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
» Fitting Store Temp Sensor BM2000
» can i ajust the hot water temp on my 2000 plse ?
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum