Boilermate 2000 - Timer control for hot water is possible
2 posters
Page 1 of 1
Boilermate 2000 - Timer control for hot water is possible
If your boilermate is randomly running the boiler pump for hours or you don't like it firing up the boiler (wastefully) throughout the day to maintain the store temperature, you can modify it to use the timer to control the hot water. You would then have to use a modern digital room thermostat to control the heating but it can be done.
There is a link from the permanent live feed to the boilermate pcb, cutting this link and wiring the timer to it then adding the permanent live to the heating which is then controlled by a programmable room thermostat works.
The hot water still works and boiler pump over run works correctly. I would only advise this if you know what you are doing however.
Richard
There is a link from the permanent live feed to the boilermate pcb, cutting this link and wiring the timer to it then adding the permanent live to the heating which is then controlled by a programmable room thermostat works.
The hot water still works and boiler pump over run works correctly. I would only advise this if you know what you are doing however.
Richard
Last edited by HizerKite on Mon Jan 15, 2018 7:31 am; edited 1 time in total
HizerKite- Posts : 9
Join date : 2017-07-23
Location : Suffolk, UK
Re: Boilermate 2000 - Timer control for hot water is possible
In a lot of case why the boiler keeps running / firing up is;
Boiler is old / scaled up / dirty system.
Boiler not putting out 80c which is required.
Mike
MGC/H2O
Norfolk
Boiler is old / scaled up / dirty system.
Boiler not putting out 80c which is required.
Mike
MGC/H2O
Norfolk
Similar topics
» Boilermate 2000 Hot water timer?
» BOILERMATE 2000 with switch" Appliance control board.
» Boilermate 2000 Timer Replacement
» Using Solar With BM2000 how do i reset the boiler control temp?
» Boilermate 2000. Timer being used but heating very intermitent.
» BOILERMATE 2000 with switch" Appliance control board.
» Boilermate 2000 Timer Replacement
» Using Solar With BM2000 how do i reset the boiler control temp?
» Boilermate 2000. Timer being used but heating very intermitent.
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum