pulsacoil 2000 wont heat my water
3 posters
Page 1 of 1
pulsacoil 2000 wont heat my water
Hi my friend has a pulsacoil 2000 which has been on the blink for sometime now, starting with what seemed as sensor failures so we changed then both.
Then we found the pump was faulty so we changed that & the compression fittings above & below it.
Now the red light flashes to say its working ok, 2 then nothing then 2 etc. There is power to both immersion heaters & both seem to be working & the heat exchanger heats up.
It still only heats up the water to barely warm.
Does anyone have any idea's as its driving us mad now !!!
Then we found the pump was faulty so we changed that & the compression fittings above & below it.
Now the red light flashes to say its working ok, 2 then nothing then 2 etc. There is power to both immersion heaters & both seem to be working & the heat exchanger heats up.
It still only heats up the water to barely warm.
Does anyone have any idea's as its driving us mad now !!!
sliceofcake77- Posts : 1
Join date : 2010-04-02
Re: pulsacoil 2000 wont heat my water
Hi sliceofcake77,
Sounds like scale in the heat exchanger to me but can't be sure without answers to a load of questions:
1) Did this problem start suddenly or did the hot water get cooler over a matter of weeks?
2) Is the pump actually running when the hot tap is running cool?
3) If YES to 2), what is the voltage at the pump terminals when the pump is running?
4) Is the water level in the header tank correct?
Cheers, Mike
Sounds like scale in the heat exchanger to me but can't be sure without answers to a load of questions:
1) Did this problem start suddenly or did the hot water get cooler over a matter of weeks?
2) Is the pump actually running when the hot tap is running cool?
3) If YES to 2), what is the voltage at the pump terminals when the pump is running?
4) Is the water level in the header tank correct?
Cheers, Mike
Sounds like calcium build up on the PHE circulation side
Sounds like calcium build up on the PHE circulation side. Confirm the pump is spinning and you installed a grundfos 15-50x18
Similar topics
» Pulsacoil 2000 -Hot water in the thermal store but cold water from the taps.
» Pulsacoil 2000 - no hot water, everything looks ok!!
» Pulsacoil 2000 - No hot Water
» Not hot water from Pulsacoil 2000
» Pulsacoil 2000 - no hot water
» Pulsacoil 2000 - no hot water, everything looks ok!!
» Pulsacoil 2000 - No hot Water
» Not hot water from Pulsacoil 2000
» Pulsacoil 2000 - no hot water
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum