No hot water in Systemate 111 but central heating is fine
Hi there
My boiler is working fine, and my central heating is fine as well. However, I get no hot water from any taps or shower. Can you please tell me what I should be looking for and whether I would need to call a plumber out.
Also, for emergency, we sue emersion heater to heat up the water. The Systemate 111 water tank heats up but still no hot water comes out of the taps or shower. Any help much appreciated.
Quick response much appreciated since we do not have any hot water.
Thanks
My boiler is working fine, and my central heating is fine as well. However, I get no hot water from any taps or shower. Can you please tell me what I should be looking for and whether I would need to call a plumber out.
Also, for emergency, we sue emersion heater to heat up the water. The Systemate 111 water tank heats up but still no hot water comes out of the taps or shower. Any help much appreciated.
Quick response much appreciated since we do not have any hot water.
Thanks
artemis- Posts : 4
Join date : 2010-07-03
Re: No hot water in Systemate 111 but central heating is fine
Artemis,
Do you mean no water AT ALL from the hot taps, or the water coming from the hot taps is cold?
Whichever, I think you need a thermal store repair specialist. The average plumber takes one look at these and flakes out on you.
Where are you?
Mike
Do you mean no water AT ALL from the hot taps, or the water coming from the hot taps is cold?
Whichever, I think you need a thermal store repair specialist. The average plumber takes one look at these and flakes out on you.
Where are you?
Mike
Re: No hot water in Systemate 111 but central heating is fine
Hi Mike
I get water but it's cold water. Do you think it's the mixing/blending valve or plate heat exchanger valve?
I'm based in Kingston Upon Thames.
Thanks
I get water but it's cold water. Do you think it's the mixing/blending valve or plate heat exchanger valve?
I'm based in Kingston Upon Thames.
Thanks
artemis- Posts : 4
Join date : 2010-07-03
Re: No hot water in Systemate 111 but central heating is fine
Artemis,
We can rule out the the plate heat exchanger (provided the water flow rate from the taps is normal and not heavily reduced). On a systemate III that still leaves a number of other possibilities unfortunately. In order of likelihood:
1) DHW sensor failure
2) PHE return sensor (if yours has one) failure
3) Flow switch failure
4) Control board failure
If I were on site, first I'd test the flow switch using a multimeter. Then if OK I'd fit a new DHW sensor to rule it out as it is such a common fault (the DHW sensor status reported by the control board cannot be relied upon). Then I'd wire in a new PHE sensor and finally, if still not working, plug in a new control board from stock. None of these quick to do for a DIYer as you need the parts.
I can come to KoT and do it if you wish. Give me a call on 07866 6766364.
Cheers, Mike
We can rule out the the plate heat exchanger (provided the water flow rate from the taps is normal and not heavily reduced). On a systemate III that still leaves a number of other possibilities unfortunately. In order of likelihood:
1) DHW sensor failure
2) PHE return sensor (if yours has one) failure
3) Flow switch failure
4) Control board failure
If I were on site, first I'd test the flow switch using a multimeter. Then if OK I'd fit a new DHW sensor to rule it out as it is such a common fault (the DHW sensor status reported by the control board cannot be relied upon). Then I'd wire in a new PHE sensor and finally, if still not working, plug in a new control board from stock. None of these quick to do for a DIYer as you need the parts.
I can come to KoT and do it if you wish. Give me a call on 07866 6766364.
Cheers, Mike
Re: No hot water in Systemate 111 but central heating is fine
What would be the total likely repiar cost for your service Mike?
Thanks
Thanks
artemis- Posts : 4
Join date : 2010-07-03
Re: No hot water in Systemate 111 but central heating is fine
Artemis,
Mike is right with the list of above parts but without an engineer testing the systemate III it's like finding a needle in a haystack with the lights off!
It could also be a faulty Mixing Valve!
Gary
M K Group
Mike is right with the list of above parts but without an engineer testing the systemate III it's like finding a needle in a haystack with the lights off!
It could also be a faulty Mixing Valve!
Gary
M K Group
Re: No hot water in Systemate 111 but central heating is fine
Hi all,
Just to let you know, got the problem fixed. British Gasd engineer replced the pump and it works fine now.
Thx
Just to let you know, got the problem fixed. British Gasd engineer replced the pump and it works fine now.
Thx
artemis- Posts : 4
Join date : 2010-07-03
Similar topics
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
» Hot water from taps for about 2 mins then lukewarm, Central heating works fine.
» Systemate 2000 no central heating
» no central heating on systemate 2000
» help me! heating works fine but only 5 mins of hot water
» Hot water from taps for about 2 mins then lukewarm, Central heating works fine.
» Systemate 2000 no central heating
» no central heating on systemate 2000
» help me! heating works fine but only 5 mins of hot water
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum