Boilermate 2000 - heating on all the time
4 posters
Page 1 of 1
Boilermate 2000 - heating on all the time
Hi - I would really appreciate some advice on a problem with my Boilermate 2000. Have had it for 7 years with no problem but today the central heating has stuck permanently on even though the room thermostat is turned as low as possible and the timer on the Boilermate is set to 'off'. Taking a look at the front panel:
1) The green 'Power On' light is not on
2) The LED display says 'On' with just the middle horizontal LED bar (store) lit up
3) The green LED lights are lit up for boiler, boiler pump on AND heating pump on
I can't check the temperature settings because when I press SW2 or SW1 nothing happens.
From reading other topics on here I'm wondering if the ACB board has gone, but am hoping it's something simpler and cheaper!!
Brian
1) The green 'Power On' light is not on
2) The LED display says 'On' with just the middle horizontal LED bar (store) lit up
3) The green LED lights are lit up for boiler, boiler pump on AND heating pump on
I can't check the temperature settings because when I press SW2 or SW1 nothing happens.
From reading other topics on here I'm wondering if the ACB board has gone, but am hoping it's something simpler and cheaper!!
Brian
wildcampion- Posts : 7
Join date : 2010-08-17
Re: Boilermate 2000 - heating on all the time
Hi Brian
Sorry to be the bearer of bad news, but yes, the processor on the ACB has certainly crashed.
You could try and re-boot the board by going through the commissioning sequence using jumper number 5, but generally the board will need replacing.
We cover the East/West Midlands if you need our help
Sorry to be the bearer of bad news, but yes, the processor on the ACB has certainly crashed.
You could try and re-boot the board by going through the commissioning sequence using jumper number 5, but generally the board will need replacing.
We cover the East/West Midlands if you need our help
Thanks - know any Merseyside Boilermate experts?
Thanks for the advice David - things have now got worse - no hot water or heating and the digital display has died. Unfortunately, we are not in your area. If you or anyone else knows of someone in Merseyside who could replace the ACB I'd be very grateful. Out of 3 plumbers tried so far, one didn't know anything about Boilermates and two haven't called back! Or is it possible for a numpty like me to replace the ACB? I can only do the most basic DIY but I'd be willing to give it a go!
Brian
Brian
wildcampion- Posts : 7
Join date : 2010-08-17
Re: Boilermate 2000 - heating on all the time
Brian,
My system had nearly the same simptoms. When I switched it off or switched off just boiler to cut bill, then next time i switch it on PCB behaves strangly, doesn't react on SW and heating was on for hours until PCB returns into normal state. I suspect some capasitors got dry so when you switch on processor was not reset properly. It is like Skybox, having it plugged into mains for years it works but as soon as you disconnect it from mains it doesn't start(the PSU). Anyway, having some capasitors ready i'm waiting for the next fault to come, although don't have it for months. For you it will be easier to replace PCB. It is very straight forward, just check jumpers and connection on old one and connect the same way new one. Or leave system on for hours(may be day) and hopefully PCB will restart.
Alex
My system had nearly the same simptoms. When I switched it off or switched off just boiler to cut bill, then next time i switch it on PCB behaves strangly, doesn't react on SW and heating was on for hours until PCB returns into normal state. I suspect some capasitors got dry so when you switch on processor was not reset properly. It is like Skybox, having it plugged into mains for years it works but as soon as you disconnect it from mains it doesn't start(the PSU). Anyway, having some capasitors ready i'm waiting for the next fault to come, although don't have it for months. For you it will be easier to replace PCB. It is very straight forward, just check jumpers and connection on old one and connect the same way new one. Or leave system on for hours(may be day) and hopefully PCB will restart.
Alex
scorp- Posts : 77
Join date : 2010-07-07
same problem
Hi there
I have the same problem however
After removing the font
1) The green 'Power On' light is not on
2) The LED display says 'On' with just the middle horizontal LED bar (store) lit up
3) none of the green LED lights are lit up for boiler
When I press SW2 or SW1 the temp is displayed and I can confirm there are no problems with the hot water.
Like the previous poster I am led to believe this is a faulty ACB but I was hoping it wasn’t.
You mention going through the commissioning sequence again, perhaps I am being daft here but I have had a look at the technical manual and it doesn’t mention anything to do with jumper 5 just that it should be checked jumper 1,3,4 should be connected.
Would you be able to explain what you meant about jumper 5 so I can try and reboot the board.
Many thanks in advance
I have the same problem however
After removing the font
1) The green 'Power On' light is not on
2) The LED display says 'On' with just the middle horizontal LED bar (store) lit up
3) none of the green LED lights are lit up for boiler
When I press SW2 or SW1 the temp is displayed and I can confirm there are no problems with the hot water.
Like the previous poster I am led to believe this is a faulty ACB but I was hoping it wasn’t.
You mention going through the commissioning sequence again, perhaps I am being daft here but I have had a look at the technical manual and it doesn’t mention anything to do with jumper 5 just that it should be checked jumper 1,3,4 should be connected.
Would you be able to explain what you meant about jumper 5 so I can try and reboot the board.
Many thanks in advance
Flashmaster- Posts : 5
Join date : 2010-10-03
Similar topics
» boilermate 2000 turned off on thermostat and overide on time clock to off
» Boilermate 2000 - no heating
» boilermate 2000 no heating or hot water
» Boilermate 2000 Hot water Ok - but No heating.
» Boilermate 2000 only heating to 70 degrees C.
» Boilermate 2000 - no heating
» boilermate 2000 no heating or hot water
» Boilermate 2000 Hot water Ok - but No heating.
» Boilermate 2000 only heating to 70 degrees C.
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum