Heating does not come on even with over ride
2 posters
Page 1 of 1
Heating does not come on even with over ride
LindaShipley posted this on the general boiler mate forum on Sat Dec 28, 2013 6:39 pm I realsie this should be on the A class forum.
.When the control circuit is switched on with both hot water and heating rocker switches on constant, the control system shows a flashing dot (indicating controller working ok). The external digistat thermostat shows a need for heat but V1.4(stat call for heat) does not light up nor does H2.2 (CH pump on). If the control circuit is turned off and on again these light show for a few seconds, the pump runs and then switches off.
Over ride makes no difference.
The hot water and boiler works fine.
I live in Dronfield near Sheffield.
Please can anyone help?.
.When the control circuit is switched on with both hot water and heating rocker switches on constant, the control system shows a flashing dot (indicating controller working ok). The external digistat thermostat shows a need for heat but V1.4(stat call for heat) does not light up nor does H2.2 (CH pump on). If the control circuit is turned off and on again these light show for a few seconds, the pump runs and then switches off.
Over ride makes no difference.
The hot water and boiler works fine.
I live in Dronfield near Sheffield.
Please can anyone help?.
LindaShipley- Posts : 4
Join date : 2013-12-28
Location : Dronfield nr Sheffield
Re: Heating does not come on even with over ride
Sounds like Main ACB.
Have you looked on home page for an advertiser in your area?
Google up Gledhill repairs in your area.
Mike
Have you looked on home page for an advertiser in your area?
Google up Gledhill repairs in your area.
Mike
Thank you for your fast response
I have followed your advice and had contact from connectheating who I hope will sort this out after the holiday. Linda.
LindaShipley- Posts : 4
Join date : 2013-12-28
Location : Dronfield nr Sheffield
Had to resort to Gledhill
I had to take out a year contract for £354 to get an engineer to come. He tried replacing the main board to no avail. The problem was eventually traced to a lower voltage signal between the thermostat and the boilermate. When the thermostat was bridged out it worked fine. We had to buy another thermostat at over £100 and now the heating is back to normal. Expensive lesson.
LindaShipley- Posts : 4
Join date : 2013-12-28
Location : Dronfield nr Sheffield
Re: Heating does not come on even with over ride
Hi Linda,
So you resorted to Gledhill then at £354:00p.
Fixed price repair.
And 1 years breakdown cover parts and labour as well?
Mike
So you resorted to Gledhill then at £354:00p.
Fixed price repair.
And 1 years breakdown cover parts and labour as well?
Mike
Similar topics
» Heating does not come on even with over ride
» Thermostat over ride
» Systemmate 2000 - heating on continuously but only one one heating circuit
» central heating on when water heating up?
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
» Thermostat over ride
» Systemmate 2000 - heating on continuously but only one one heating circuit
» central heating on when water heating up?
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.