No Hot Water
Hi
Having a problem with our boilermate 2000
The only way we can get hotwater is to have our central heating on very high over 22deg
Previous to this in the summer months heating has been off and we have had plenty of water on demand when needed, and has been like that for last 6 years
There are no leaks that i can see, the cistern is full, timer is perm on, LCD display shows "on"
Mrs is getting a bit peeved, ideas? or decent repair service for South Wales
Having a problem with our boilermate 2000
The only way we can get hotwater is to have our central heating on very high over 22deg
Previous to this in the summer months heating has been off and we have had plenty of water on demand when needed, and has been like that for last 6 years
There are no leaks that i can see, the cistern is full, timer is perm on, LCD display shows "on"
Mrs is getting a bit peeved, ideas? or decent repair service for South Wales
TMS- Posts : 6
Join date : 2011-04-10
Re: No Hot Water
Ok display shows "-on" when i take front panel off
When hot water tap turned on the display chages to "=on" and there is a slight buzzing noise but nowt that sounds like a pump working
Does that make sense?
When hot water tap turned on the display chages to "=on" and there is a slight buzzing noise but nowt that sounds like a pump working
Does that make sense?
TMS- Posts : 6
Join date : 2011-04-10
Re: No Hot Water
Hi,
With the tap on check the far right hand side pump, remove the silver screw on the front and check that it is spining on the inside.
If the pump is spining then check the store temperature by pressing the sw2 button on the PCB board.
If the store is above 70 degrees then you will be looking at replacing the dhw / phe sensors.
If not come back to me.
Kind regards
Gary
MK Group Ltd
With the tap on check the far right hand side pump, remove the silver screw on the front and check that it is spining on the inside.
If the pump is spining then check the store temperature by pressing the sw2 button on the PCB board.
If the store is above 70 degrees then you will be looking at replacing the dhw / phe sensors.
If not come back to me.
Kind regards
Gary
MK Group Ltd
Re: No Hot Water
took the middle silver large slotted screw out, small trickle of water then with tap on as i tightedned it back up could here water going through it
Checked temp reading says 85! is changing the dhw / phe sensors something easy to do or require a specialist? cost wise?
Checked temp reading says 85! is changing the dhw / phe sensors something easy to do or require a specialist? cost wise?
TMS- Posts : 6
Join date : 2011-04-10
Re: No Hot Water
They are easy enough to do, cost about £30.00 each plus delivery, available from Segel or Keep the heat on.
Re: No Hot Water
so i'm looking for a Gledhill GT153 DHW Sensor ? are there any idiot guides out there? cant find a picture of it so cant relate it to what i see on the boiler
TMS- Posts : 6
Join date : 2011-04-10
Re: No Hot Water
Ah think i fig out.. is it the white lead coming from the left hand side of pump unit? Does water need to be off on install? will boiler reset or do i need to do anything once i have the new part? ie: will the 85 reading drop back down to 70?
TMS- Posts : 6
Join date : 2011-04-10
Re: No Hot Water
Change both the dhw and phe sensor which are either side of the plate heat exchanger (white leads with Brass ends). turn the mains water off and have an old towel at the ready!
Turn the power off when changing them.
hope this helps
Kind regards
Gary
MK Group Ltd
Turn the power off when changing them.
hope this helps
Kind regards
Gary
MK Group Ltd
Re: No Hot Water
Was there a link or image above? i cant see anything
TMS- Posts : 6
Join date : 2011-04-10
Re: No Hot Water
Sorry could get image to work, if you click on the link below...
http://www.gledhill-spares.net/documents/BM2000-Iss10.pdf
Go to page 6, you will be changing part no 7 - 8 as shown on the diagram.
Kind regards
Gary MK Group Ltd
http://www.gledhill-spares.net/documents/BM2000-Iss10.pdf
Go to page 6, you will be changing part no 7 - 8 as shown on the diagram.
Kind regards
Gary MK Group Ltd
Similar topics
» Pulsacoil 2000 -Hot water in the thermal store but cold water from the taps.
» Only short blasts of hot water in the morning, rarely hot water in the afternoon/evening
» No hot water, red fault light on, after adjusting thermostat
» Gledhill Boilermate Class A OV - PHE (hot water) pump constantly whirring, but no hot water
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
» Only short blasts of hot water in the morning, rarely hot water in the afternoon/evening
» No hot water, red fault light on, after adjusting thermostat
» Gledhill Boilermate Class A OV - PHE (hot water) pump constantly whirring, but no hot water
» Boilermate 2000 hot water and store temperature fine until you switch the central heating on and the store temperature drops below 60 stopping central heating but Hot water still works.
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum