Post  TMS Sun Apr 10, 2011 8:02 am

Hi

Having a problem with our boilermate 2000

The only way we can get hotwater is to have our central heating on very high over 22deg

Previous to this in the summer months heating has been off and we have had plenty of water on demand when needed, and has been like that for last 6 years

There are no leaks that i can see, the cistern is full, timer is perm on, LCD display shows "on"

Mrs is getting a bit peeved, ideas? or decent repair service for South Wales

TMS

Posts : 6
Join date : 2011-04-10

Back to top Go down

No Hot Water Empty Re: No Hot Water

Post  MK Group Ltd Sun Apr 10, 2011 8:21 am

Check if pump is coming on when tap is opened.

Kind regards

Gary
MK Group Ltd
MK Group Ltd
MK Group Ltd

Posts : 301
Join date : 2010-04-03

http://www.mkgroupltd.co.uk

Back to top Go down

No Hot Water Empty Re: No Hot Water

Post  TMS Sun Apr 10, 2011 9:50 am

Ok display shows "-on" when i take front panel off

When hot water tap turned on the display chages to "=on" and there is a slight buzzing noise but nowt that sounds like a pump working

Does that make sense?

TMS

Posts : 6
Join date : 2011-04-10

Back to top Go down

No Hot Water Empty Re: No Hot Water

Post  MK Group Ltd Sun Apr 10, 2011 10:04 am

Hi,

With the tap on check the far right hand side pump, remove the silver screw on the front and check that it is spining on the inside.

If the pump is spining then check the store temperature by pressing the sw2 button on the PCB board.

If the store is above 70 degrees then you will be looking at replacing the dhw / phe sensors.

If not come back to me.

Kind regards

Gary

MK Group Ltd

MK Group Ltd
MK Group Ltd

Posts : 301
Join date : 2010-04-03

http://www.mkgroupltd.co.uk

Back to top Go down

No Hot Water Empty Re: No Hot Water

Post  TMS Sun Apr 10, 2011 11:15 am

took the middle silver large slotted screw out, small trickle of water then with tap on as i tightedned it back up could here water going through it

Checked temp reading says 85! is changing the dhw / phe sensors something easy to do or require a specialist? cost wise?

TMS

Posts : 6
Join date : 2011-04-10

Back to top Go down

No Hot Water Empty Re: No Hot Water

Post  MK Group Ltd Sun Apr 10, 2011 11:45 am

They are easy enough to do, cost about £30.00 each plus delivery, available from Segel or Keep the heat on.
MK Group Ltd
MK Group Ltd

Posts : 301
Join date : 2010-04-03

http://www.mkgroupltd.co.uk

Back to top Go down

No Hot Water Empty Re: No Hot Water

Post  TMS Sun Apr 10, 2011 1:01 pm

so i'm looking for a Gledhill GT153 DHW Sensor ? are there any idiot guides out there? cant find a picture of it so cant relate it to what i see on the boiler

TMS

Posts : 6
Join date : 2011-04-10

Back to top Go down

No Hot Water Empty Re: No Hot Water

Post  TMS Sun Apr 10, 2011 1:08 pm

Ah think i fig out.. is it the white lead coming from the left hand side of pump unit? Does water need to be off on install? will boiler reset or do i need to do anything once i have the new part? ie: will the 85 reading drop back down to 70?

TMS

Posts : 6
Join date : 2011-04-10

Back to top Go down

No Hot Water Empty Re: No Hot Water

Post  MK Group Ltd Sun Apr 10, 2011 2:04 pm

Change both the dhw and phe sensor which are either side of the plate heat exchanger (white leads with Brass ends). turn the mains water off and have an old towel at the ready!

Turn the power off when changing them.

hope this helps

Kind regards

Gary
MK Group Ltd
MK Group Ltd
MK Group Ltd

Posts : 301
Join date : 2010-04-03

http://www.mkgroupltd.co.uk

Back to top Go down

No Hot Water Empty Re: No Hot Water

Post  MK Group Ltd Sun Apr 10, 2011 2:05 pm

[url][/url][img][/img]

MK Group Ltd
MK Group Ltd

Posts : 301
Join date : 2010-04-03

http://www.mkgroupltd.co.uk

Back to top Go down

No Hot Water Empty Re: No Hot Water

Post  TMS Mon Apr 11, 2011 1:51 am

Was there a link or image above? i cant see anything

TMS

Posts : 6
Join date : 2011-04-10

Back to top Go down

No Hot Water Empty Re: No Hot Water

Post  MK Group Ltd Mon Apr 11, 2011 4:22 am

Sorry could get image to work, if you click on the link below...

http://www.gledhill-spares.net/documents/BM2000-Iss10.pdf

Go to page 6, you will be changing part no 7 - 8 as shown on the diagram.

Kind regards

Gary MK Group Ltd
MK Group Ltd