A class is tripping power in the house
I woke up four days ago with no power in the house and as soon as you turn the boiler mate a series on it trips the power in the house again, I have had a couple of people look at it and they changed one of the pumps but it is still doing the same thing, any ideas?
Paul Atkinson- Posts : 4
Join date : 2013-11-03
Re: A class is tripping power in the house
Which system?
Paul Atkinson- Posts : 4
Join date : 2013-11-03
Re: A class is tripping power in the house
Seriel number 0020052251 boilermate ov a class
Paul Atkinson- Posts : 4
Join date : 2013-11-03
Re: A class is tripping power in the house
Boilermate Open vented.
What boiler?
I would check for any burnt wires / cables.
Check the back up heater and associated controls.
Next disconnect the pumps safely! 1 at a time.
Then disconnect the boiler wiring from the unit.
It may well be your boiler
Mike
What boiler?
I would check for any burnt wires / cables.
Check the back up heater and associated controls.
Next disconnect the pumps safely! 1 at a time.
Then disconnect the boiler wiring from the unit.
It may well be your boiler
Mike
Similar topics
» Power in the house keeps tripping out
» Boilermate A Class tripping and not sending power to Glowworm Boiler
» Pulsacoil A-Class Boiler - No power
» Pulsa Coil A Class off peak power relay burnt out
» MCB 2 Tripping
» Boilermate A Class tripping and not sending power to Glowworm Boiler
» Pulsacoil A-Class Boiler - No power
» Pulsa Coil A Class off peak power relay burnt out
» MCB 2 Tripping
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum