Boilermate II green light on constantly

2 posters

Go down

Boilermate II green light on constantly Empty Boilermate II green light on constantly

Post  Jonos Wed Jan 20, 2010 6:40 am

For some reason the green light at the bottom of my boilermate II stays on continuously so I have to turn off the boiler at the mains.
When it is powered on the hot water and heating work fine but I can`t regulate the temperature of the heating, the room thermostat in the living room has no effect whatever setting it is on. The Potterson boiler itself fires up every 20 minutes or so for about 10 minutes. It doesn`t seem to matter what setting the clock on the boilermate is on either so I have replaced it woth a brand new Grasslin clock and it doesn`t appear to have made any difference.

Any ideas would be greatly appreciated.

Jon

Jonos

Posts : 5
Join date : 2010-01-20

Back to top Go down

Boilermate II green light on constantly Empty Re: Boilermate II green light on constantly

Post  THERMAL SOLUTIONS Wed Jan 20, 2010 10:29 am

is your gas boiler thermostat set to maximum ?
turn off your heating set the boilermate thermostat to minimum and see if it shuts off.
it maybe a defective thermostat, try that 1st though.
hope this helps
mark.
www.gledhill-repair.co.uk

THERMAL SOLUTIONS

Posts : 54
Join date : 2009-12-31
Age : 60
Location : cambridgeshire

http://www.gledhill-repair.co.uk

Back to top Go down

Boilermate II green light on constantly Empty Re: Boilermate II green light on constantly

Post  Jonos Thu Jan 21, 2010 3:20 am

Thanks, I tried setting boiler to max and boilermate to min but the green light stayed on.
I even tried to calibrate it with the instructions on the front of the boilermate to no avail. Do you think it is likely to be the boilermate thermostat? (am I right thinking this is the dial on the boilermate controling the storage temp which has the capillary bulb thermostat attached by thin wire?). Is it best to change this before I start to look at the 2 PCBs on the front panel of the boilermate?

Regards

Jon

Jonos

Posts : 5
Join date : 2010-01-20

Back to top Go down

Boilermate II green light on constantly Empty Re: Boilermate II green light on constantly

Post  THERMAL SOLUTIONS Thu Jan 21, 2010 11:36 pm

yes mate sounds like the stat to me.
let me know how you get on.
regards
mark.
www.gledhill-repair.co.uk

THERMAL SOLUTIONS

Posts : 54
Join date : 2009-12-31
Age : 60
Location : cambridgeshire

http://www.gledhill-repair.co.uk

Back to top Go down

Boilermate II green light on constantly Empty Re: Boilermate II green light on constantly

Post  Jonos Fri Jan 22, 2010 10:03 am

Cheers Mark, I just needed some expert advice but suspected as much.
I`ve ordered a new thermostat and will let you know the outcome after I`ve fitted it.

cheers

Jon

Jonos

Posts : 5
Join date : 2010-01-20

Back to top Go down

Boilermate II green light on constantly Empty Re: Boilermate II green light on constantly

Post  Jonos Sun Jan 31, 2010 4:41 am

I received new thermostat yesterday and fitted it ok. Once the boilermate gets up to temperature the green light goes out and the downstairs boiler stops firing. Problem I have now is that I still can`t seem to control the heating from either the room stat or the clock on the boilermate (I bought a new Graslin clock a few weeks ago). Heating still comes on if the clock is set to off or set to timed and it`s outside the times for the heating to come on. In order to stop boiler calling for demand I have to reduce store temp setting on boilermate to turn the green light off.

Any ideas grateful

Jon

Jonos

Posts : 5
Join date : 2010-01-20

Back to top Go down

Boilermate II green light on constantly Empty Re: Boilermate II green light on constantly

Post  Sponsored content


Sponsored content


Back to top Go down

Back to top

- Similar topics

 
Permissions in this forum:
You cannot reply to topics in this forum