Boilermate TS140 fault
2 posters
Page 1 of 1
Boilermate TS140 fault
Hi,
I am currently using what I believe to be a Boilermate TS140. Recently, after a period of time, the central heating has been cutting out, & the digital clock / timer on the Boilermate unit resets (clock to zero, & preset switching times deleted). The unit appears to be running hotter than usual, although I may just be imagining this. A test today revealed that this reset is happening after around 40 minutes. It is possible to then switch the heating back on, & it then functions fine, but again resets after some time. Hot water does not appear affected by this malfunction.
Does anyone have any idea what could be causing this? Is it possible that the unit is overheating - & is there an inbuilt control to cut off power if this happens?
Cheers,
Rob.
I am currently using what I believe to be a Boilermate TS140. Recently, after a period of time, the central heating has been cutting out, & the digital clock / timer on the Boilermate unit resets (clock to zero, & preset switching times deleted). The unit appears to be running hotter than usual, although I may just be imagining this. A test today revealed that this reset is happening after around 40 minutes. It is possible to then switch the heating back on, & it then functions fine, but again resets after some time. Hot water does not appear affected by this malfunction.
Does anyone have any idea what could be causing this? Is it possible that the unit is overheating - & is there an inbuilt control to cut off power if this happens?
Cheers,
Rob.
Rob_Jacques- Posts : 4
Join date : 2010-07-21
Re: Boilermate TS140 fault
Hi Rob,
Which range Boilermate is it? TS140 is not a lot of help! A II, a III, a 2000,or an A-Class?
Sounds like a clock failure and a new clock/timer will fix it. OR possibly a power supply problem. What boiler is connected to it? (Make and model?)
Cheers, Mike
Which range Boilermate is it? TS140 is not a lot of help! A II, a III, a 2000,or an A-Class?
Sounds like a clock failure and a new clock/timer will fix it. OR possibly a power supply problem. What boiler is connected to it? (Make and model?)
Cheers, Mike
Re: Boilermate TS140 fault
Hi Mike,
Thanks for the prompt response. I'm not sure which Boilermate range our unit falls under, we inherited the current set up when we moved to this property around a year ago, & we don't have the original documention. The above is a photo of the unit in question. The boiler we're using is a Myson Orion.
[img][/img]
Cheers,
Rob.
Thanks for the prompt response. I'm not sure which Boilermate range our unit falls under, we inherited the current set up when we moved to this property around a year ago, & we don't have the original documention. The above is a photo of the unit in question. The boiler we're using is a Myson Orion.
[img][/img]
Cheers,
Rob.
Rob_Jacques- Posts : 4
Join date : 2010-07-21
Re: Boilermate TS140 fault
Sorry, should be a bit easier to view the photo now.
[img][/img]
Cheers,
Rob.
[img][/img]
Cheers,
Rob.
Rob_Jacques- Posts : 4
Join date : 2010-07-21
Re: Boilermate TS140 fault
Ok, that's a Boilermate Original. Very few of them left now!
Simple appliance. The heating pump is powered by the clock via (I think) the pump delay timer board. The Boilermate Original may not have that delay timer board actually but I can't remember, it may have been first introduced on the Boilermate II.
This sort of fault is most easily diagnosed by the 'parts swapping' technique. Change the clock and the delay board (if it has one) together for a 100% certain fix. If economy is important then I'd change the timer first and see if the problem persists. If it does, I'd put the old timer back and change the delay board.
If there is no delay timer board then it HAS to be a clock/timer fault. It will not be anything to do with the Orion boiler.
Cheers, Mike
Simple appliance. The heating pump is powered by the clock via (I think) the pump delay timer board. The Boilermate Original may not have that delay timer board actually but I can't remember, it may have been first introduced on the Boilermate II.
This sort of fault is most easily diagnosed by the 'parts swapping' technique. Change the clock and the delay board (if it has one) together for a 100% certain fix. If economy is important then I'd change the timer first and see if the problem persists. If it does, I'd put the old timer back and change the delay board.
If there is no delay timer board then it HAS to be a clock/timer fault. It will not be anything to do with the Orion boiler.
Cheers, Mike
Re: Boilermate TS140 fault
Hi Mike,
We opted to change the timer unit first & see if that solved the issue & thankfully since doing that everything seems to be working again. The old timer unit wasn't properly fixed to the surrounding housing, & so it pushed back onto the inner skin of the boilermate every time a button was pressed - once removed the unit looked somewhat worse for wear. It appeared that the heat may have fried it over time...
Thanks for all of your help,
Cheers,
Rob.
We opted to change the timer unit first & see if that solved the issue & thankfully since doing that everything seems to be working again. The old timer unit wasn't properly fixed to the surrounding housing, & so it pushed back onto the inner skin of the boilermate every time a button was pressed - once removed the unit looked somewhat worse for wear. It appeared that the heat may have fried it over time...
Thanks for all of your help,
Cheers,
Rob.
Rob_Jacques- Posts : 4
Join date : 2010-07-21
Similar topics
» Boilermate BMA 185 fault code 29
» BoilerMate or Boiler at fault?
» boilermate a class fault codes
» A Class Boilermate ov Fault code 31
» Boilermate 2000 Suspected Intermittent PCB Fault
» BoilerMate or Boiler at fault?
» boilermate a class fault codes
» A Class Boilermate ov Fault code 31
» Boilermate 2000 Suspected Intermittent PCB Fault
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum