Boilermate 3
Hi we have been without hot water for about a week now.It seems that there is no hot water in the tap or shower,the shower runs warm for about 1 minute then goes cold.The boiler down stairs seems to be working because the flame comes on as it should.What advice can you give me any would be a help,we live in the North East of England.
Kevin- Posts : 4
Join date : 2009-02-10
Re: Boilermate 3
Hi Kevin,
If the central heating works then we know the Boilermate is warming up correctly. Does it?
If it does, we next need to find out if the HW pump runs when you turn a hot tap ON. Does it?
If yes, then it's probably blender valve failure. If not, then it's probably sensor failure or flow switch failure.
Hope that helps, but unfortunately there is no substitute for being in front of the appliance when homing in on a fault!
Cheers, Mike
If the central heating works then we know the Boilermate is warming up correctly. Does it?
If it does, we next need to find out if the HW pump runs when you turn a hot tap ON. Does it?
If yes, then it's probably blender valve failure. If not, then it's probably sensor failure or flow switch failure.
Hope that helps, but unfortunately there is no substitute for being in front of the appliance when homing in on a fault!
Cheers, Mike
Re: Boilermate 3
thanks for the sugestion about the cold water pipe bypass it worked a treat cost about 350 pounds and hopefuly will keep us in hot water.
Kevin- Posts : 4
Join date : 2009-02-10
Similar topics
» Boilermate II.
» New to Boilermate...
» boilermate II
» alternating hot and cold water
» replacing boilermate 111
» New to Boilermate...
» boilermate II
» alternating hot and cold water
» replacing boilermate 111
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum