Post  rudy gadalla Fri Feb 27, 2009 4:18 am

radiators tend to be gravitating,when room stat is off ,

rudy gadalla

Posts : 4
Join date : 2009-02-26

Back to top Go down

boiler mate ii Empty Re: boiler mate ii

Post  Mike the Boilerman Fri Feb 27, 2009 4:54 am

Hi rudy,

There should be a check valve in the same pipe as the central heating pump, to stop that happening. Yours is either not working or missing.

Cheers, Mike

Mike the Boilerman
Admin

Posts : 447
Join date : 2009-01-08

https://gledhill-repairs.forumotion.net

Back to top Go down

boiler mate ii Empty rudy ceck valve

Post  rudy gadalla Fri Feb 27, 2009 7:16 pm

thanks Mike yes there is no check valve in my system will update you on that when ihave one fitted. KInd regards Rudy

rudy gadalla

Posts : 4
Join date : 2009-02-26

Back to top Go down

boiler mate ii Empty rudy check valve

Post  rudy gadalla Sat Feb 28, 2009 2:35 am

Iforgot to ask is there a check valve that you recommend

rudy gadalla

Posts : 4
Join date : 2009-02-26

Back to top Go down

boiler mate ii Empty ref boiler mate II

Post  rudy gadalla Mon Mar 09, 2009 7:20 pm

Dear mike I have had a check valve fitted but after two days every thing was fine , about 00,30this am yes the heating come & the clock was set to come on at 07.30am any more ideas why this could be happening please.kind regards rudy