no hot water
I went to use the shower earlier today and the water gradually got colder, and now there is no hot water, i checked the cistern, which was very low. I have now refilled the cistern to a sufficient level, but still no hot water. The red led, on the control board, is flashing normally at 2 flashes per second. When i try the hot water at a tap the boiler makes a buzzing sound which hasnt happened before. Can you help me in solving the problem.
wallis- Posts : 1
Join date : 2009-01-12
Re: no hot water
Hi Wallis,
The boiler (or more specifically, the control board) makes a buzzing sound when running the pump, during HW demand. You probably haven't noticed it before with the boiler front in place and you in the bathroom running a tap.
The pump is probably air-locked if the unit got so empty of water that it stopped working. Try loosening the big silver screw in the centre of the pump while it is running and see if any air comes out.
Cheers, Mike
The boiler (or more specifically, the control board) makes a buzzing sound when running the pump, during HW demand. You probably haven't noticed it before with the boiler front in place and you in the bathroom running a tap.
The pump is probably air-locked if the unit got so empty of water that it stopped working. Try loosening the big silver screw in the centre of the pump while it is running and see if any air comes out.
Cheers, Mike
wallis wrote:I went to use the shower earlier today and the water gradually got colder, and now there is no hot water, i checked the cistern, which was very low. I have now refilled the cistern to a sufficient level, but still no hot water. The red led, on the control board, is flashing normally at 2 flashes per second. When i try the hot water at a tap the boiler makes a buzzing sound which hasnt happened before. Can you help me in solving the problem.
Possible shower cartridge fault
If it is only your shower that seems to have this problem but all taps are working, it could be your shower cartridge that is faulty.
Similar topics
» Pulsacoil 2000 -Hot water in the thermal store but cold water from the taps.
» Only short blasts of hot water in the morning, rarely hot water in the afternoon/evening
» No hot water, red fault light on, after adjusting thermostat
» Gledhill Boilermate Class A OV - PHE (hot water) pump constantly whirring, but no hot water
» Poss reason for no hot water - Check the water level at the top of the unit
» Only short blasts of hot water in the morning, rarely hot water in the afternoon/evening
» No hot water, red fault light on, after adjusting thermostat
» Gledhill Boilermate Class A OV - PHE (hot water) pump constantly whirring, but no hot water
» Poss reason for no hot water - Check the water level at the top of the unit
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum