Boilermate II
Hi all, I am after some much needed advice. I currently have mild DHW and luke warm CH. The property is 20 years old and we have been here for 2 so I doubt the system has been maintained etc. The external overflow pipe seems to drip when the heat is called for through the room stat. Last few days however the thermal store has been stone cold yet both pumps are running. The in and out of both pumps are luke warm yet the pumps themselves are hot.
I’ve removed the lid from the f&e tank and the water is currently around the level on the outer casing. Any tips into fault finding would be great!
Much appreciated, Dan
I’ve removed the lid from the f&e tank and the water is currently around the level on the outer casing. Any tips into fault finding would be great!
Much appreciated, Dan
Dan1206- Posts : 2
Join date : 2020-03-30
no heat
If the pipes into both pumps are cold then surely the issue is with the heat source which I assume is the boiler? Has the boiler tripped out or gone off for some other reason? Regards Murray
Re: Boilermate II
Martin, thank you for your reply.
I have a Potteron suprima 3 boiler, currently the green neon is flashing as well as igniting every now again where it goes into a solid green.
I have a Potteron suprima 3 boiler, currently the green neon is flashing as well as igniting every now again where it goes into a solid green.
Dan1206- Posts : 2
Join date : 2020-03-30
boiler
OK sound no red led to indicate an error. I assume you can tell that the boiler is lighting as well. Next question is what temperature is the water coming out of the boiler? Hopefully you can feel the pipes obviously you would expect them to be to hot to touch for long as a minimum when the boiler is running. If they are not the issue is probably with the boiler, if the boiler is not heating the water sufficiently then you are on a non-starter for hot water and heating. Regards Murray
Re: Boilermate II
this may be a silly question, have you tried adjusting the blender valve to see if this improves the DHW temp?
Geths- Posts : 30
Join date : 2010-11-24
Similar topics
» Wanted - Boilermate engineer in Southampton area
» Which boilermate is this?
» boilermate 2 how old is old
» Boilermate 3
» BOILERMATE OV
» Which boilermate is this?
» boilermate 2 how old is old
» Boilermate 3
» BOILERMATE OV
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum