Systemate 2000 - Pump continually on.

2 posters

Go down

Systemate 2000 - Pump continually on. Empty Systemate 2000 - Pump continually on.

Post  ianbams Sun Jun 19, 2011 10:30 am

The system is about 7 years old and works as it should. However, one of the pumps seems to be working 24/7 and produces a pulsating throbbing which is particularly noticeable at night. Surely, this shouldn't happen? Also from time to time the system 'rattles and rolls' like an old steam engine, but it quietens down after 15-20 minutes. Any ideas?

ianbams

Posts : 7
Join date : 2011-06-19

Back to top Go down

Systemate 2000 - Pump continually on. Empty Re: Systemate 2000 - Pump continually on.

Post  MK Group Ltd Mon Jun 20, 2011 11:08 am

Hi,

have you checked that the F & E tank is topped up with water.

Kind regards

Gary

MK Group Limited.
MK Group Ltd
MK Group Ltd

Posts : 301
Join date : 2010-04-03

http://www.mkgroupltd.co.uk

Back to top Go down

Systemate 2000 - Pump continually on. Empty Re: Systemate 2000 - Pump continually on.

Post  ianbams Tue Jun 21, 2011 10:18 am

Gary,

Many thanks - have done that recently and I think it has stopped the 'steam engine' effect. However, still have the pulsating throbbing noise which has to be a pump, but it's on all the time!

Cheers.

ianbams

Posts : 7
Join date : 2011-06-19

Back to top Go down

Systemate 2000 - Pump continually on. Empty Re: Systemate 2000 - Pump continually on.

Post  MK Group Ltd Tue Jun 21, 2011 10:53 am

Can you check what temperature the store is reaching via the pcb board?
MK Group Ltd
MK Group Ltd

Posts : 301
Join date : 2010-04-03

http://www.mkgroupltd.co.uk

Back to top Go down

Systemate 2000 - Pump continually on. Empty Re: Systemate 2000 - Pump continually on.

Post  ianbams Tue Jun 21, 2011 10:55 am

Gary,

Many thanks, but I'm no engineer!!! PCB Board??

Cheers,

Ian.

ianbams

Posts : 7
Join date : 2011-06-19

Back to top Go down

Systemate 2000 - Pump continually on. Empty Re: Systemate 2000 - Pump continually on.

Post  MK Group Ltd Tue Jun 21, 2011 11:05 am

Take the front cover off and look at the printed circuit board, press the sw2 button once and tell me the value.

MK Group Ltd
MK Group Ltd

Posts : 301
Join date : 2010-04-03

http://www.mkgroupltd.co.uk

Back to top Go down

Systemate 2000 - Pump continually on. Empty Re: Systemate 2000 - Pump continually on.

Post  ianbams Tue Jun 21, 2011 1:18 pm

55

ianbams

Posts : 7
Join date : 2011-06-19

Back to top Go down

Systemate 2000 - Pump continually on. Empty Re: Systemate 2000 - Pump continually on.

Post  MK Group Ltd Wed Jun 22, 2011 12:36 am

If the store is only reaching a temperature of 55 then the unit will continually ask for heat from the boiler and the pump will continuously run.

You need to now find out if it is a fault with the boiler or the SysteMate, check the temperature with a thermometer at the top of the boiler (flow pipe) usually the right hand pipe and at the SysteMate centre pump.

Come back to me with your findings and we can go from there.
MK Group Ltd
MK Group Ltd

Posts : 301
Join date : 2010-04-03

http://www.mkgroupltd.co.uk

Back to top Go down

Systemate 2000 - Pump continually on. Empty Re: Systemate 2000 - Pump continually on.

Post  ianbams Fri Jun 24, 2011 2:09 am

Thanks for your help! Will get back to you as soon as I can find a thermometer!!

ianbams

Posts : 7
Join date : 2011-06-19

Back to top Go down

Systemate 2000 - Pump continually on. Empty Re: Systemate 2000 - Pump continually on.

Post  ianbams Thu Jun 30, 2011 7:16 am

Hi again, I now have a thermometer. Both temps are at about 42C. Checked SW2 button again and that was reading 60.

ianbams

Posts : 7
Join date : 2011-06-19

Back to top Go down

Systemate 2000 - Pump continually on. Empty Re: Systemate 2000 - Pump continually on.

Post  MK Group Ltd Thu Jun 30, 2011 7:49 am

Is your boiler thermostat on Max?
MK Group Ltd
MK Group Ltd

Posts : 301
Join date : 2010-04-03

http://www.mkgroupltd.co.uk

Back to top Go down

Systemate 2000 - Pump continually on. Empty Re: Systemate 2000 - Pump continually on.

Post  ianbams Thu Jun 30, 2011 7:54 am

It's on about two thirds.

ianbams

Posts : 7
Join date : 2011-06-19

Back to top Go down